Discuss Motor earth in the UK Electrical Forum area at ElectriciansForums.net
I’ve recently seen a motor wired directly from the local isolator to the motor terminal box in 3 core 1.5mm cable. The gland has been made off into a threaded hole in the motor terminal box and at the isolator end directly connected to the incoming swa from the MCC by means using a flylead. My question is is this a sufficient for earthing the motor. My understanding is you can use the armour as a cpc but wasn’t sure if any additional “fly leads” should be fitted at the motor end?
it may well be ok, have you tested the earth continuity?
there is little point in adding a fly lead if the gland is directly screwed into the device.
years ago, and it is still possible now but rarely done,
entire installations were done in rigid steel conduit.
the conduit would be the earth, all the cables inside would be phase or neutral.
extra earth cables were rarely added as the earth resistance through the conduits was normally better than you could achieve with an earth cable of equal or smaller csa to the live conductors.
the only time fly leads were added was if the fitting or device being powered needed an earth and it was not directly bolted to the conduit.
because they have always done it like this,
think back to basics, if you have a bolted connection to the motor terminal box, that is then bolted to the motor itself, you are likely to have a better connection and lower resistance than any fly lead could achieve.
also, if the terminal box is plastic then a fly lead would be required.
Thank you James
Reply to Motor earth in the UK Electrical Forum area at ElectriciansForums.net
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
I'm about to replace the cable from a starter to an existing 2hp 3-phase 3-wire motor adjacent. The motor is rigidly bolted to a bed and has a...