I’ve recently seen a motor wired directly from the local isolator to the motor terminal box in 3 core 1.5mm cable. The gland has been made off into a threaded hole in the motor terminal box and at the isolator end directly connected to the incoming swa from the MCC by means using a flylead. My question is is this a sufficient for earthing the motor. My understanding is you can use the armour as a cpc but wasn’t sure if any additional “fly leads” should be fitted at the motor end?
 
it may well be ok, have you tested the earth continuity?

there is little point in adding a fly lead if the gland is directly screwed into the device.
 
it may well be ok, have you tested the earth continuity?

there is little point in adding a fly lead if the gland is directly screwed into the device.
Yeah earth continuity from the motor terminal earth to the isolator is coming up as 0.01 ohms
 
years ago, and it is still possible now but rarely done,

entire installations were done in rigid steel conduit.
the conduit would be the earth, all the cables inside would be phase or neutral.

extra earth cables were rarely added as the earth resistance through the conduits was normally better than you could achieve with an earth cable of equal or smaller csa to the live conductors.

the only time fly leads were added was if the fitting or device being powered needed an earth and it was not directly bolted to the conduit.
 
because they have always done it like this,

think back to basics, if you have a bolted connection to the motor terminal box, that is then bolted to the motor itself, you are likely to have a better connection and lower resistance than any fly lead could achieve.

also, if the terminal box is plastic then a fly lead would be required.
 
because they have always done it like this,

think back to basics, if you have a bolted connection to the motor terminal box, that is then bolted to the motor itself, you are likely to have a better connection and lower resistance than any fly lead could achieve.

also, if the terminal box is plastic then a fly lead would be required.
Thank you James
 

Reply to Motor earth in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock