Pendant light? With most ceilings being around 2.4m, that's going to be a very short drop in most cases.
A batten holder might keeps things high enough, or a gallery fitting of some sort, but agree that IP44 or greater is preferable.
Always considered it strange that the 2.25m is measured from the floor, even over a bath. I've seen baths fitted with legs fully extended and the legs on wooden blocks to help with drainage problems.
Depends on the location of the (Pendant) doesn’t it when your standing in the bath with a shower then ceiling height is reduced and especially if the pendant is within arms reach. All bathrooms without suitably IP rated light should be rcd protected in my opinion if they aren’t they C2 if they do have suitable IP rated light without rcd protection then C3. Easy to resolve isn’t it don’t have a pendant/batten holder in bathroom simple
 
Can’t comment on the thermal damage as I cant see it. Photo would help.

IP rated bathroom light.

A common mistake among some sparkies.
if it’s above=2.25M it does not need to have a water resistant fitting. A normal pendant is fine.

i would advise getting a bathroom IP rated light, but would not code it if it’s above that 2.25M.
get your tape measure out.
I thought a batten fitting is acceptable
 
Thanks everyone for your comments. The outcome:
I asked the report writer to change 'no RCD protection to lighting circuits' from C2 to C3. Not having heard back, I went down the route of sending the report as it stood, plus photos, to 3 other trusted electricians, and getting quotes for remedial work. One of these suggested using RCBOs instead of replacing the CU. Have gone with him because I'm saving hundreds of pounds. Today the original writer got back to me. Gave me a quote for using RCBOs (much higher than other quote) Then he said he'd change the C2 to C3. Declined because by then I'd had enough hassle, and lost my patience....
 
Depends on the location of the (Pendant) doesn’t it when your standing in the bath with a shower then ceiling height is reduced and especially if the pendant is within arms reach. All bathrooms without suitably IP rated light should be rcd protected in my opinion if they aren’t they C2 if they do have suitable IP rated light without rcd protection then C3. Easy to resolve isn’t it don’t have a pendant/batten holder in bathroom
Curiously, it doesn't the 2.25m measurement is still from the floor, even if the lamp is diretly over the (raised) bath. Ridiculous, but that's what the regs say.
 
Curiously, it doesn't the 2.25m measurement is still from the floor, even if the lamp is diretly over the (raised) bath. Ridiculous, but that's what the regs say.
Yea I agree is ridiculous I just change existing light fitting to suitably ip rated one is easy to do with little extra £££ so don’t see the need to be lazy and not change It.
 
The old reg. said must be not in reach of a person in a bath or shower*. This would exclude a non IP rated light over a raised bath.

* This reminded me of one of the funniest things I've ever witnessed. A electricity board inspector, who had a personal feud with the householder, was inspecting my new installation. I had place an immersion heater switch outside of the airing cupboard in a very large bathroom. Bath position had been revised after I'd done the electrics, and the sight of this overweight character balancing in the bath, desperately trying to prove this switch was within reach, had to be seen to be believed.
 
The old reg. said must be not in reach of a person in a bath or shower*. This would exclude a non IP rated light over a raised bath.

* This reminded me of one of the funniest things I've ever witnessed. A electricity board inspector, who had a personal feud with the householder, was inspecting my new installation. I had place an immersion heater switch outside of the airing cupboard in a very large bathroom. Bath position had been revised after I'd done the electrics, and the sight of this overweight character balancing in the bath, desperately trying to prove this switch was within reach, had to be seen to be believed.
?
 
The property was a 'time warp' large farmhouse, which was sold at auction. The boss man of the local electricity board and my customer were the last two bidders, and my customer outbid him, so when it came to connect up to the mains supply (place had a small generator only), he came out in person to do the checks.
Only thing he found 'wrong' in the end, was that I had used the earthing stud on the side of a large ironclad generator change over switch to join some bonding wires together, instead of a separate service block or MET.
 
The property was a 'time warp' large farmhouse, which was sold at auction. The boss man of the local electricity board and my customer were the last two bidders, and my customer outbid him, so when it came to connect up to the mains supply (place had a small generator only), he came out in person to do the checks.
Only thing he found 'wrong' in the end, was that I had used the earthing stud on the side of a large ironclad generator change over switch to join some bonding wires together, instead of a separate service block or MET.
Nice to hear stories like that Brian, Although you are definitely old school with the wording of “Electricity Board” they havnt changed much these days just less competent ?
 
Things were much simpler in those days.
SWEB installed the supply, SWEB fitted the meter, SWEB did some very basic testing, SWEB energised the supply, SWEB turned up every three months to read the meter, and SWEB sent you your electricity bill.
 
Things were much simpler in those days.
SWEB installed the supply, SWEB fitted the meter, SWEB did some very basic testing, SWEB energised the supply, SWEB turned up every three months to read the meter, and SWEB sent you your electricity bill.
Yea I bet is too many ppl sticking their dirty fingers in the pie these days isn’t it
 

Reply to EICR unsatisfactory due to 'no RCD protection to lighting circuits' in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock