Discuss Metal steps secured to concrete (bonding) in the UK Electrical Forum area at ElectriciansForums.net
newfutile
We have had 2 metal steps installed to cover main supply cables (out to flats) from a Ryefield .
when measured IR from MET to steps i got 0.091 MegOhms.
The usual calculations are for when a 30 ma RCD is protecting (which is not the case here)
91 Kohm is above the usual value of 23 Kohm I usually use (10ma).
Should these be bonded to earth?
I wouldn't earth it. As you say using the equations the maximum current that flows through the body is < than 10mA.
Using the formula from GN8:
rearranged to:
I get 2.5mA when taking ZT as 1000ohms as suggested in the guidance.
Are there any other earthed parts within touching distance? GN 8 states "Consequently, for a conductive part to be able to introduce a potential to a person (or livestock) in contact with the potential of any of the conductive parts, that part should be accessible to such a person (or livestock)." I assume this would also apply to your situation.
(I am referencing the 17th ed amd 2 of guidance note 8)
Reply to Metal steps secured to concrete (bonding) in the UK Electrical Forum area at ElectriciansForums.net
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
4K
Yes, still doubting my own judgement when it comes to supp bonding and EICRs, so would welcome any thoughts on the latest one. Newish flat...
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
6K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
I hear many views of people who believe that DPF's and CDPF's fitted to their vehicles are a problem and many people resort to removing them, or...
8K