    What do I search for on Amazon: WIFI continuity Switch No current, no load

    I have a bathroom fan with a moisture detector that turns it on and off. It also has a control circuit to turn it on/off when moisture is not connected. This is a no voltage/no current circuit. I want to add a parallel control circuit that would of course be no load no current that I can turn...
  2. cliffed

    Cpc no continuity on pendants

    EICR picked up no continuity on cpc on 3 pendants fittings in a grd Floor Flat. Zs measured @ other pendants & complies. Different opinions on the coding personally a C2 for me..but others are saying C3 mainly because of the code guidance in code breakers. I think this statement relates to no...
  3. D

    Voltage and Continuity Tester Recommendations

    Hi all, Firstly I am new to the forum, so will start by saying hi. I work as an electricians mate, and am joining the forum to gain experience. I am looking to purchase a decent voltage and continuity tester that complies with GS38. The two I have considered so far are the Kewtech KT1780 and...
  4. HappyHippyDad

    Continuity where you would not expect continuity!

    I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but I did. I haven't even finished the first fix and the metal back box does not have an earth connected to it yet. The voltage tester (on resistance...
  5. S

    Continuity values keeps going down.

    So bought a second hand Megger BM233 to practice with as I'm a college student.. So I was just using it on a loose 2.5 cable. Testing on the neutral from both sides . Whilst having the device on the Ohm side. I nulled it to zero by touching the probes. When I do the dead test. It starts off...
  6. A

    Megger MIT420/2 unstable continuity readings?

    Chaps - having problems with a new Megger MIT420/2 insulation/continuity tester 'oscillating' and failing to give stable resistance readings in continuity mode with some motors (although it did it once on a Cal Card!). I don't think it's a duff unit, but anyone else have one and experienced...
  7. king185

    Continuity / Ohms testing help / Short ?

    Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe there is a problem with the cable (possibly between E and N), and I have used a multi-meter to do some checks on the CU (shed side) and below you will...
  8. S

    Cheap Voltage and continuity tester?

    Hey guys I am still studying in college. I just need one to play around with. As I will be making my own boards at home. Can anyone recommend me one to use ? So I can start practicing how to do testing. Thanks
  9. Conan The Librarian

    Earth to Neutral Continuity - Advice Needed

    Hi all. Reasonably competant non electrical engineer homeowner here. I have a question for the experts: I recently replaced a horrible above-ceiling downlight connection with a proper Hager junction box. Whilst checking things generally I found my multimeter was reading a continuity between...
  10. Neptune

    Continuity test after Ring Circuit

    After completing a new RFC or modifying an existing one, I will always test continuity across all 3 conductors at the Consumer unit. I use the continuity function on my Fluke 2 pole tester to do this. This is done whilst the circuit is dead. Prior to this, I am very diligent with the conductors...
  11. u2v2w2

    Contactors lost continuity

    What could be the reason for all of the three Siemens contactors on a 37kW star delta starter to lose continuity on auxiliary contacts and main contacts all at once? Probably the best thing to do is to replace them since cleaning would be too fiddly. There are no signs of water intrusion only...
  12. Yp510n

    continuity test on a protective bonding conductor

    Hope i find someone who can help me with this one. I have this question on an exam: A continuity test on a protective bonding conductor gives a result of 15ohms. What possible reasons for the result and what actions (if any) that should be taken? My answers where: -wrong size conductor shows...
  13. M

    Am2s Continuity Of Protective Conductors

    In the am2s assessment where do I write the Continuity Of Protective Conductors test results? Where on the test sheet do I add the results?
  14. B

    Low earth resistance continuity test

    I’ve just carried out a continuity test on a rfc. And I’m getting a lower earth resistance Reading than the reading on both the live and neutral wires. its a circuit in a house converted into two flats and the circuit is wired in 2.5/1.5 twin and earth. Live and neutral are both 0.46 earth is...
  15. R

    R1,R2,Rn versus r1,r2,rn continuity readings on EICR.

    Looking at the EICR form. GENERIC SCHEDULE OF TEST RESULTS Looking for clarification on R1,R2,Rn versus r1,r2,rn continuity values. I have reached the some conclusions. Do r1,r2 and rn only apply to ring circuits and R1,R2 and Rn (not on form) to radial? It just looks like that might be the...
  16. S

    TP & N Continuity & Polarity

    Just practicing for my AM2. When testing a 3P and N socket, as I understand, R1 to R2 is CPC to any live (L1, L2, L3) to prove continuity, but how do you prove polarity?
  17. B

    Cheap Continuity tester?

    What values of resister and led would work in series with a cheap tone generator, and a 9V? Only needed to check unpowered wiring circuits for shorts.
  18. T

    Best way to check continuity of cpc for lighting

    20 y old lighting circuit with cpc at the board but terminating into class 2 recessed down light fittings. Looks like there is a junction box in the ceiling void feeding the light with L&N but I can't access the junction box so not sure how can prove continuity of the circuit?
  19. N

    Coincidence? Continuity?

    Hello, Back in November I had a dedicated circuit installed for a garage door opener. Over the next few days and ever since I noticed my dryer would sometimes be blinking "PF" (power fail). The breaker was never tripped and by the time I'd notice the error code on the dryer, everything would be...
  20. I

    No continuity of neutral conductor

    On the sockets ring. What you advise, go round all sockets? Checking netruals

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock