insulation resistance test

  1. D

    Stage 2 insulation resistance test

    I have installed a circuit for an oven and carried out all of the relevant testing so far. Apart from a neon on the double pole isolation switch, there is no current using equipment connected to the circuit yet as the property is empty. In this situation, would one just make a note on the...
  2. J

    Insulation resistance test

    Evening chaps, I've been asked to do a visual inspection, and an insulation resistance test on a fishing boat, which is working off 24v, this is a new ruling apparently, and without me signing it off as ok, the boat is currently docked, and not allowed to go out fishing. The visual checks...
  3. T

    Low Insulation Resistance readings N-E

    Looking for some guidance here. I'm currently shadowing a guy and we're testing a new extension on a school. 3 phase TNCS supply from the original busbar. Feeds a section board and from the section board it feeds 4 3 phase DB's. The DBs have one feed in and then split to a separate power and...
  4. Neptune

    Insulation resistance test on a damaged conductor

    I have a 2 metre T&E cable. I applied a IR test (500v) across P and N to E with the other end of the cable safely sitting on the floor and it reported the meter maximum. As expected. I then completely cut through the N conductor on the cable and repeated the test. It still reports the meter...
  5. Pegasus

    Insulation Resistance Test, trying to wrap my head around it

    I am self-teaching fault-finding and testing, but I can't wrap my head around insulation resistance tests. From my understanding you send 500V for domestics down the conductors using an Multi-Function Tester, and the values should be over 1M Ohm, now my question is why should the resistance be...
  6. D

    How do you disconnect neon lights in sockets while doing insulation resistance test.

    Hello everyone, I was just wondering how do you disconnect neon lights from socket outlets when doing insulation resistance test, as this will effect the readings, thanks.
  7. K

    Low Insulation resistance test on smoke detectors

    Hi Everyone Just a question bothering me as you cannot do Insulation resistance test on smoke detectors as they can become damaged so obviously smoke detectors are sensitive but they are also installed on lighting circuit so if perform low insulation resistance test 250V between Live and...
  8. D

    Is it ok to do insulation resistance test on RCBO at 500v?

    I know you are not supposed to do a insulation test on circuits that are protected by an RCD at 500v because it may damage the electronic components inside the RCD so that's why you switch the RCD off before you test the individual circuits, however, what if the circuits are all protected by...
  9. D

    UK Low Insulation Resistance Test

    Hi guys, Hoping someone can clarify some things here. I had a socket replaced in my kitchen recently and as part of this, the electricians did an Insulation Resistance test and told me the reading was very low at just over 1 mega ohms. They advised me to basically rewire the ring (at...
  10. mak

    Insulation resistance test on a ring final circuit

    Might be trivial question. My understanding is that we test on either leg of the ring since both legs make up a radial, but some say they test both legs at once, i.e. LL to NN, it would make sense if the other leg is not insulated since this is a live test, but I don't see why not if the other...
  11. M

    What are the implications of a failed Neutral - Earth insulation resistance test?

    Greetings! Newbie here! We have 3 phase installation in our Lighting dimmer rack. During Insulation Resistance testing on Earth-Nuetral, readings was 0.33Mohm on 500v test. What causede the failed test and how can I troubleshoot? Thank you! Markus
  12. D

    Quinetic controller ok with 500v insulation resistance test?

    Hello Everyone Hopefully the title is self explanatory. Or should I disconnect it for the test?
  13. T

    Insulation resistance test on length of SWA cable

    Doing new supplies for a school new Shneider 3 phase & N MCCB panel board. 50mm 4 core SWA one end made off in the board earth fly lead from banjo to earth terminal. The other end gland made off in gland (fly lead not made off yet) 3 phases and neutral just hanging there. Done installation...
  14. N

    insulation resistance test on shower circuit with neon isolater

    On a new install of a shower circuit, with a neon isolater, is it better to use choc blocks to bypass neon isolater or would it be ok to just test live-earth (live being neutral and live combined) and miss the live-live test? If testing just live-earth, would you write it down in details of...
  15. naylorpd

    Insulation resistance test issue

    Back in 2013 I had a Domestic Electrical Installation Condition Report done on my rented property - nothing horribly major but one thing I didn't understand... I had a C3 code for "0 ohms readings for I.R test for sockets & lighting (unable to remove all loads sockets, lighting had electronic...
  16. T

    How to bypass an RCD and carry out an insulation resistance test on a circuit

    Hi all. I'm a 4th year electrician currently awaiting to finish my trade test. (FICA in Scotland) the only parts I have to pass is the testing part and fault finding. I'm currently studying testing as this is something I have done the minimum of onsite. Could someone tell me how I would...
  17. L

    Insulation Resistance test question?

    Hi guys, I have what may seem a basic question. If a cable has been skinned at some point along the circuit would an IR test pick that up in the readings? Many thanks
  18. B

    3 Phase Insulation Resistance Test on motor & TP & N skt help

    Looking for some advice on how to carry out a IR test on a 3-phase motor and a TP & N skt, these are parts of a module I have failed on a test and am looking to see where I am going wrong and what the normal procedure for carrying out this test would be?
  19. 1

    Insulation resistance test

    Hi all on a eicr insulation resistance test between live conductors to earth gn3 says join l & n and test to earth is there any difference between that and testing phase to earth then neutral to earth? As you guys know some boards are a right mess and not in order to locate which belongs to which
  20. S

    500v Insulation Resistance Test ok?

    Hi all, still training so please forgive my very simple question. Why is it ok to test an appliance at 500vdc when PAT testing but great care should be taken to remove all equipment when IR verifying a new circuit installation? Is it simply just because connected equipment will make a nonsense...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock