ring final

  1. A

    Fault on Ring final circuit

    Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not contactable. I need to fix this asap. Ring final circuit tripping. I am not clueless and I have some test gear. Can fully isolate the supply with an...
  2. B

    Shower on 4mm ring final circuit.

    Hi, I've got a customer who wants a 10.5 kW shower installed in his bathroom. As it happens he already has two unused 4mm T&E cables run from the CU cupboard to the loft. I know it's unconventional but is there any reason I can't use these cables to make a dedicated RFC for just the shower...
  3. S

    Help with Ring Tabulated Current Equation

    Hi there I am struggling with the following calculation. 4mm Ring Final Circuit, In = 32A Cg - group of 6 with a correction factor of 0.57 Ci - 50mm insulation of 0.78 It = In/CgCi It = 32/0.57x0.78 It = 71.97A Then I get stuck here: Ib < In < It < Iz 4mm Cable from Table 4E2A gives Iz of...
  4. S

    Loading on an existing Kitchen and living room 32amp ring final

    Bit of advise if anyone has time.. I have a customer who brought a new kitchen from wrens. Customer has had the route to the kitsch redecorated 6months ago. I’ve found a route which means 25meter going externally and I quoted to supply new 6mm and ring circuit. They are supplying Oven (13amp...
  5. J

    How would you meter (kwh) a ring final

    I have a customer that requested kwh meters on the socket circuits of an office lock he rents out,(rooms are rented separately). There are two 16amp radials which obviously are not an issue, But the ring mains 4 of are causing me a headache for obvious reasons! The question is how would you guys...
  6. C

    why would i get 0.00 on Ring Final for R1+RN?

    Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite r1's+rn's for figure of 8 joined in connector blocks. set up Kewtech KT63 multifunction tester nulled leads and plug adapter and tested at sockets at...
  7. S

    Ring Final discussion

    Hi all, I had a fault on site today I've not encountered before. if anyone could shed some light on a similar fault they may have encountered before that would be helpful. I was changing some damaged socket fronts over and I noticed the cables had signs of over heating so I thought I would do a...
  8. M

    Maintenance Free 32A Junction Box

    I've been looking at the Wagobox, specifically the 221-4 box, and noticed that it is only classed as maintenance free if the current is 20A or less (derating factor applied to the 32A capacity of the Wago 221 Series 4 connectors) and has a tie-wrap fitted. Do you know of any Wago maintenance...
  9. W

    Wiring of ring final circuit

    Always ask fellow sparks this and always get different answers, what do you feel the quickest way of wiring a ring in say a flat for example. Do you piggy back it round getting your 2 legs into each room before dealing with the wiring of the sockets in each room. Or do you just wire to each...
  10. T

    Ring final routing in loft conversion

    Good evening All. Maintenance electrician here moving into domestic installations. What I'm still struggling with is the ring finals routing, especially in loft conversions. I am wiring one at the moment. Can you please have a look at the diagram below. Apologies it's very basic and rooms are...
  11. T

    Running ring final cables in loft eaves

    Hi All. I am wiring a loft conversion and want to avoid covering cables in the insulation. I can clip the cables to the studs on the other side of the wall in the zone parallel to the socket outlets. Is this sensible thing to do or would you rather run in the holes through the joists and apply...
  12. V

    Have come across a 16A Ring Final

    I've not come across this before. The current regs state it should be on a 32A MCB. I've been asked to re-wire a bedroom which will involve extending this ring. It already serves two other bedrooms and the lounge. I know I probably should tell the client to upgrade this MCB to 32A, but is it...
  13. J

    UK Find a Fault on a Ring Final Circuit

    I am not a qualified electrician, I was employed as an electrician after my MoD electronics apprenticeship but that was 30 odd years ago. So I have basic skills and an insulation tester with a low resistance capability. This is an old installation with a new cu installed in 2014 (EICR etc...
  14. M

    C&G Level 3 Project Question (Cafe ring final sockets length)

    Hi guys I'm a bit frazzled by the wording on the main project. So, we are told to keep the max circuit length down to 30m, tutors said that isnt physically possible so just try to keep it under 40m and they noted that the socket circuit was a bit of a mental one and that the 30m guidance set...
  15. I

    Ring final circuit Zs.

    Can you get the zs by using a earth loop impedance tester. I was taught if there's 2 rings circuits, you can do r1,r2, rn /4 on 1 On the other ring you can plug in the earth loop impedance tester and measure the zs. If you do it that way you must write in the observations you measured. Have I...
  16. V

    CPC low R2 continuity reading ring final

    Hi, I've just been testing a ring final before installing an outdoor socket and I got an R1 and rn of 0.6, but instead of 1.01 for R2 I got a range of readings from 0.1 to 0.51 and it wouldn't settle down, so I couldn't continue the tests. I know parallel paths could cause a low reading, but...
  17. R

    Extension of ring final circuit

    Hi there all, I have a property and I have noticed the following wiring (please see below) in one of the rooms in the house. It looks like the ring circuit has been extended. A single 2.5mm Twin + Earth cable (in red) is providing power from the consumer unit which feeds a chain of electrical...
  18. timhoward

    Insulation resistance difference both ends of ring final cct

    Initial fault was RCD tripping, narrowed down to a ring final cct. IR tests on that cct with all loads removed were showing almost zero between neutral and cpc. So I broke the ring apart and eventually found the nail through a cable, and got that all sorted. Now its testing ok in as much as...
  19. T

    4mm ring final circuit

    Evening all Pricing a bungalow that has 300mm insulation in the roof, as im going to be wiring around the corenrs as much as i can and through the middle would you use 4mm on the ring final circuits? I want to use 2.5mm radials for bedrooms and living room but my boss is old school and wants...
  20. V

    Ring Final Test - Neutral >19.99kOhms

    Just checking, what I think I already believe. Doing a pre-install test of some outdoor sockets on a ring final. So far, confirmed bonding, incoming polarity, Ze and Pfc and RCD Test on circuit, everything fine and within regs. However on testing Ring Final, Line came out fine (0.7), Neutral...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock