  1. R

    Pump wired in 2.5mm on a shower circuit 10mm on Type B 40 acceptable ?

    Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me thinking I have seen a circumstance at work, where: A shower has been wired in 10mm T+E on a 40A breaker. But then from the shower isolator switch a 2.5mm...
  2. G

    Recommendation request for Type B distribution board

    As a retired electrician, I need to specify a new type B board for a village church. Principal load is heating. Ipfc phase to phase is 1.1kA. Requirements: 23 final circuits, so don't want to exceed an 8 way board - pref no higher than about 625mm. SPD therefore not to steal 3 MCB positions...
  3. S

    Recommend me a Type B (3 Phase) Distribution Board

    Need to source Type B 3-phase distribution & 3P MCBs for EVSE, 1P RCBOs etc. so my sparky can install. A 6-way 3P board will suffice. Wondering what the general concensus is. Say, Contactum at the cheaper end vs Schneider Acti9 at the upper end. Drawn towards the Schneider as super neat...
  4. GBDamo

    UK Type B RCDs for fire protection?

    Hi all, not been around in a while but I'm working through a quote at the moment and found this at the end of the equipment (AC kit) suppliers quote. From the icons provided were definately talking B type and not B curve. For the job in question this one paragraph statement could add...
  5. H

    Type b RCD and Matt:e

    Hi all I need an RCD replaced in my consumer unit... It's type .... Down the line, I'll be getting an EV charger installed with a Matt:e device between the unit and the charger.... Do I need a type b RCD, or can I just replace the type a, with the protection being provided by the Matt:e device...
  6. N

    Type B rcbos and inrush current

    Does any one have a rough idea how many 24w led panel 600x600 could go on a 10 amp type b rcbo with out tripping or a 6 amp type B rcbo I found a long circuit that complies with zs when a direct measurement is taken at its furthest point , but on length alone im sure it does not comply by...
  7. D

    UK MCB type confusion.

    I've noticed at my grandparents house that all the MCB's in the consumer unit are all type C, every single one of them. Including the ring final circuits and lighting (there's no fluorescent lights in the house at all). The house isn't that old as well. Maybe about 16 years old. With me being a...
  8. M

    Variable voltage 220v Appliance (Type I) to 110v (Type B) socket,

    Hello everybody, I am not an electrician or anything of the sort, but figured that this would be the best place to ask my question. I have a 220v heating appliance with a Chinese Type I plug. The appliance has a volatge regulator knob that allows voltage to be varied anywhere between 0v and...
  9. Bubbler Bob

    Upgrading Older Style Wylex Type B MCB's to BS EN 60898

    hanks Hi new member here wishing some advise! I've a 6 Way Consumer Unit with Wylex Type B (WYB Series, BS3871) Push In/Pop Out style MCB's, which is working with no known faults. Utilising 2 x 5A MCB's re front & rear ceiling light circuits, and 2 x 30A MCB's re front & rear power socket...
  10. C

    MCB Timer that fits Proteus type B din rail?

    In my garage I have a Proteus mcb consumer unit. There is some garden lighting directly attached to a B20 single pole. No switch ! have to walk 100ft in the dark , open the garage and flick on the MCB to get the lights on. Such a bizarre installation. The cable runs under concrete , no chance of...
  11. M

    Gewiss MCB 32a type B.

    Does anyone have any b32 lying around that aren't needed? I am after 2, happy to pay postage and some beer tokens TIA
  12. J

    Student BS60898 Type B trip question

    Hello I'm a Level 2 electrical installations student and I have a question about Type B BS60898 circuit breakers. I've been revising tonight and have noticed that the trip time on these is 3 to 5 times the rated current. What does this mean? Say I had a 32A Type B would it trip over any...
  13. 1capybara

    Who makes this: type B, TP+N panels for DIN rail breakers and dual RCDs ?

    Who makes a TP+N panel, bigger than a consumer unit, for example, 14-way (with space for 12 or 14 three-phase breakers). It should feed its outgoing breakers using bus bars, not wires. (I call this a Type B panel) And it should be usable for Dual RCDs, one for the left side of the panel and one...
  14. A

    lighting circuits- Type B or Type C MCB

    What do you guys tend to use Type B MCB for lighting circuits but know that some use Type C even when the loadings are low. What do others prefer and why?
  15. S

    Wanted - mem memera 2000 ab mcb 20a type b 6ka bs3871

    Hi fellas, Anybody got any of these breakers kicking about in unit/garage? Trawled ebay but no joy as yet MEM MEMERA 2000 AB MCB 20 AMP TYPE 2 & B M6 BS3871 DELTA CIRCUIT BREAKER
  16. K

    ZS for Push button Wylex 3871 Type B fuses

    Hi, I have old style Wylex push button breakers at CU, and these are labelled as BS 3871, Type B and are 5 & 30 amps. I can not find any ZS values in the regs for these, but see these labelled as N/A. Any help apprecriated. Thanks
  17. N

    Crabtree Starbreaker Type B RCBO's (various amperage)

    Hello, just listed some spare rcbo's on eBay that I have and don't need anymore. Selling them cheap and thought it may help some of you guys out. http://www.ebay.co.uk/itm/271106453049?var=&ssPageName=STRK:MESELX:IT&_trksid=p3984.m1558.l2649 Thanks.
  18. C

    (MIDLANDS) For Sale: 40 RCBO's - Hager Type C & Eaton MEM type B.

    Having a clear out of excess stock after a few jobs have ended as I have no room for them, and wont be using them again soon. All stuff is brand new & boxed. Boxes may be a little scuffed in places where they have been on site. I have for sale: RCBOS (all 30mA): Hager - 10x ADC110 10A Type C...
  19. P

    Type B or C MCB

    Can anyone help. At the moment I’m working on a library with about 11 power circuits for SSO & a CCTV/security system & 10 lighting circuits which are mostly track mounted LED spots & 2 fluorescent fittings all wired in T&E & MICC fed from a 125A TPN board. The spec calls for 10ka C type MCB or...
  20. La Poste

    Type B or C RCBO

    Greetings. Friend of mine has a fridge freezer and a standing freezer that need RCBO protection. Both these appliances run off the same socket which is a separate radial so easy to protect as it will only be these two items on this one particular circuit. I am not sure of the starting current...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock