I've tested several radial circuits and only getting 0.00 ohms on the r+r2 test (zero'd leads)
2 of the radials only supplies one socket each and are approx. 3 metres in total length. (zs 0.25 and 0.21)
Another radial only supplies one socket and is appox. 5m in length. (zs 0.35)
The final radial supplies 2 sockets and approx. 7m in total length. (zs 0.53)
Are the readings due to the length of the run or could it be the batteries need changing on my Fluke Multifunction (even though no battery warning)
3m of 2.5/1.5 will have a R1+R2 of 0.06. probably too low for your meter's resolution. try witout nulling the leads, then subtract the lead resistance from the measurement.
Thanks for the quick replies.
The Fluke Multifunction is auto ranging for the continuity tests and according to their website, on the 20 ohms scale for continuity testing it's resolution is 0.01 ohms.
So I would of thought it could read as little as 0.01 ohms.
I've heard they produce funny readings when they need new batteries but I've had no warning.
Just to prove your MFT how about fitting some replacement batteries, and see if that make any difference
and you've been a member long enough that you should know there's no such thing as r1+r2 on a radial . :6:
Or try your instrument on some lengths of spare cable and see what you get.
Compare your readings against the theoretical values in the back of the OSG.
Ha, missed that one Tel! :)
Although technically its R1+R2 for your radial circuits. Whereas you record r1+r2 around your RFC with the highest value being classed as R1+R2. Is this a play on the capital 'R' telectrix?
Reply to 0.00 ohms r1+r2 on radial circuit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Looking at the EICR form. GENERIC SCHEDULE OF TEST RESULTS Looking for clarification on R1,R2,Rn versus r1,r2,rn continuity values. I have...
7K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Hi. I have a radial circuit supplying electricity to the garage (part of the house). It's on a 20amp breaker, uses 2.5mm cable. It currently only...
9K