Discuss 0.12 ohms Suppliers ZE in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi
Just completed a rewire and doing all the testing but when I come to the External loop impedance I'm getting 0.12 ohms. I've never had a reading this low before, is there something I'm missing or is this possible?
And I have no parallel paths to make the reading lower either
Many Thanks
there should really be no reason for concern with this value. As long as you've measured it properly.
do you have a reason to believe it should be higher?
The only reason I'm asking really is that I've never had one this low before, I think the lowest i've had before this was around the 0.6 mark, so just making sure really, i'm 100% sure I'm measuring it right
Well its relative to the earthing system and proximity to distributors supply transformer (where their reference 0v earth reference point is obtained). the closer you are, the lower the resistance for the earth fault loop.
With never having read a value below 0.6 ohms before, this would suggest you most oftenly work on TN-S systems?
Had 0.08 aswell, on my first NIC assesment! looked at the assesor and said sorry, but thats what the meter says, yup, substation 30 metres away. Passed
I've had 0.00 a few times on domestic, transformer in the back garden! Very low Ze's are common on industrial sites with there own 11kv trannys
Most seemingly TNS supplies achieve below 0.15 round are way leading me to believe that its only the short leg of cable to the property that remains TNS, it must have had new mains run in underground and PME'd
0.6 is high and in 1000 tests I have never seen one that high (apart from TT).
tested a TT the other day and got 35 ohms which was good as the rod was a twig!
Test it again when the grounds frozen or dried out!! I can assure you you won't see 35 ohms then!! You could even see that 35 ohms with a nasty zero added to it...lol!!
The amount of rain you have had these past couple of months or so, i bet there are many electricians patting themselves on the back after testing these twigs...
Hi
Many Thanks
Have to agree with the others. Nothing strange at all about 0.12
35ohms or 350....with 100ma S type or a 30ma, or both, it'll still disconnect within 0.2s
Carry on patting yourselves on the back guys.
Fool!!!
So now your telling us not to even bother with ensuring ''Stability'' in a TT installation now are you??
Reply to 0.12 ohms Suppliers ZE in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
4K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...