Discuss 1.5mm SWA, Acceptable or bad practice ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
now MI is a totally different ball game, op was for opinions and thats what he got :rolleyes:
No **** that is what he got!!
So how comes MI is a different ball game, but SWA with it's higher CCC is not? Surely the same rules apply?
1.5mm MI (bare and exposed to touch, as it would be in this situation) = CCC of 23A light duty and 25A heavy duty clipped direct and 25A light duty and 26A heavy duty on tray.
1.5mm SWA 70 deg c (thermoplastic)= 21A clipped direct and 22A on tray.
1.5mm SWA 90 deg c (thermosetting)= 27A clipped direct and 29A on tray.
Most of the time nowadays I find that SWA is thermosetting insulation, and so the 27A CCC would be the one to look at. Which is better than even the heavy duty MI by 2A... So, with respect, how is MI a different ball game?
:confused::):D;)
P.S. I was being quiet Flukey, but you just wouldn't let it lie!
The op was not asking for opinions,
It was asking for the current carrying capacity of 1.5 3 core swa, this is in the brb so no opinion needed.
Also is it acceptable to run a radial in 1.5 swa to 2 x sockets on a 16 amp mcb, again verifiable in the brb so no opinion need.
What you are doing flukey is saying how you would do it, which was definatly not the op.
read my reply, acceptable but not good pactice :rolleyes: my opinion :rolleyes:
:confused::):D;)
im not playing pevvers, you can read MY opinion ;)
But why is MI a different ball game?
I'm not playing either, just curious how it's acceptable for a cable with a lower CCC to be okay to use, but one with a higher one isn't acceptable??
1.5 MI is a direct replacement for 2.5 t/e in nearly all situations, but then you would know that.:p
you have my opinion and no matter how hard you try you wont change it because thats the way I do it ;)
i have never said its not acceptable, read my posts, just not what i would do :rolleyes:
I was only joking about the futher discussions....
I'm in Broomfields in Pitsea, but I won't be stealing any business from you as I'm not on the tools anymore!
just down the road from me then, im in pitsea too, small world ;)
im open to any further discussions, just dont question my methods as theyre mine not yours :p
definitely 5 per cent beer for me too :D
I know it depends on its inststallation method but what is the max current carrying capacity of 1.5mm swa 3 core?
If im looking at the correct table 4D4A it says 18a clipped direct.
But then this manufactures spec says 32a. (page 3) http://www.alertelectrical.com/upload/pdf/329armoured.pdf
I want to know if its acceptable to run a radial to 2 x outdoor sockets using 1.5mm SWA on a 16a mcb
I would use 2.5 for 2 sockets radial
So would I, but I would actually make it an RCBO instead of an MCB.
But a 1.5mm would be fine, :rolleyes:
I have a shed [aprox 20 m long] supplied by a swa 1.5 mm coming off a household unit that will only accept domestic 3 pin plug fuses in it, so it is fused at 13 amp & perfectly acceptable by all the posts here. just wondering as my wife does tend to overload things [heater + tumble dryer etc] the fuses have blown before
This is a zombie thread. All that matters is that the overcurrent protection for your 1.5mm2 SWA is appropriate for its current carrying capacity based on reference method. Table 4D4A has the CCC of your cable at 21A when clipped direct, or 22A when buried in the ground. Your breaker/fuse needs to be rated lower than this.
Reply to 1.5mm SWA, Acceptable or bad practice ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Just taken deilvery of an Electric Car (Mini Electric) and so doing some research into installing a charge point. Supply is a standard Single...
4K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
8K
Short Version Is it permissible to have 2 feeds to 2 separate consumer units in a detached garage? Is it permissible to run SWA underground...