Discuss 10/3 120ft. Black and red On 1 breaker to keep amps up. What is the max breaker for that? in the USA area at ElectriciansForums.net

Ok, but don’t forget that if you double the conductors to the breaker (to allow for larger current?)
Then you have to double the conductors on the neutral as well.
The current on the neutral will be the same as on the live.
 
Ok, but don’t forget that if you double the conductors to the breaker (to allow for larger current?)
Then you have to double the conductors on the neutral as well.
The current on the neutral will be the same as on the live.
Yes. I had the 10/3 already. And just trying to reduce the amperage fade off. I was going to use a 15 or 20 breaker. But wanted someone else’s opinion on the breaker size and if I need to go bigger or could go bigger what y’all suggested. I think it would be fine with a 20 amp breaker but I’m curious as to what y’all would do
 
I can double the neutral if I need to with no problem
If you double the current on one side of the circuit you MUST double the other side as well. If you don’t increase the neutral then it will melt when the increased (double) load goes through it.
Not sure why you need to increase your cable size. Is it a bigger load, or is it to reduce volt drop?

I am in the UK and so I have no idea what the characteristics are of 10/3 cable. But the principles of circuit currents are the same everywhere. You must double both legs. Probably the earth too, as the earth fault path may not meet code.
 
If you double the current on one side of the circuit you MUST double the other side as well. If you don’t increase the neutral then it will melt when the increased (double) load goes through it.
Not sure why you need to increase your cable size. Is it a bigger load, or is it to reduce volt drop?

I am in the UK and so I have no idea what the characteristics are of 10/3 cable. But the principles of circuit currents are the same everywhere. You must double both legs. Probably the earth too, as the earth fault path may not meet code.
If you double the current on one side of the circuit you MUST double the other side as well. If you don’t increase the neutral then it will melt when the increased (double) load goes through it.
Not sure why you need to increase your cable size. Is it a bigger load, or is it to reduce volt drop?

I am in the UK and so I have no idea what the characteristics are of 10/3 cable. But the principles of circuit currents are the same everywhere. You must double both legs. Probably the earth too, as the earth fault path may not meet code.
First off thank you for responding to my inquiry. But…. I under stand what your saying. I did say amp drop off In my earlier reply but I meant volt drop off. Ok. So all I want to know is the max breaker so I do not burn up my wiring. I want to make sure I stay well under the max. If you don’t understand the wire I am using then you don’t know what the max breaker I can use. So saying that, you can not answer my original question. And if you can’t answer my original question then why are you even commenting at all?
 
First off thank you for responding to my inquiry. But…. I under stand what your saying. I did say amp drop off In my earlier reply but I meant volt drop off. Ok. So all I want to know is the max breaker so I do not burn up my wiring. I want to make sure I stay well under the max. If you don’t understand the wire I am using then you don’t know what the max breaker I can use. So saying that, you can not answer my original question. And if you can’t answer my original question then why are you even commenting at all?
Just pointing out a general issue in your plan and hoping you take that on board.
But I’ll leave you on your own now. Hopefully there will be someone else from your region who can help you. But I haven’t exactly seen a rush of suggestions!
Bye now.
 
The NEC does not permit paralleling conductors smaller then 1/0 see NEC article 310.10 (H) (1), which is what is being done, only way to be code compliant is to use larger conductors, and then 250.122(B) kicks in and you have to increase the size of the grounding conductor proportionately in size to the ungrounded (hot) conductor(s), it's pain in the butt rule but code is code.
 
10/3 120ft. Going to an out building. Black and red On 1 breaker to keep amps up. What is the max breaker for that setup?
You are not allowed to parallel wires if they are smaller than 1/0 wire. You need to add a 40 amp double pole breaker and use # 8 wire if your having problems with amperage with # 10 wire
 

Reply to 10/3 120ft. Black and red On 1 breaker to keep amps up. What is the max breaker for that? in the USA area at ElectriciansForums.net

Similar Threads

I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...
Replies
5
Views
902
Good afternoon - we're considering adding an additional breaker to our "main service panel" which is where the meter is located. That panel has 6...
Replies
1
Views
662
I am looking to install a dedicated breaker (20 amp) for a mini-split AC. My panel is full but I was thinking to install a tandem breaker and free...
Replies
14
Views
2K
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Replies
1
Views
194
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
580

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock