Hi,
I hope someone can help as I'm getting conflicting advice re the fitting of a 10.5kw electric shower.

my 8.5kw unit recently died and I bought a 10.5 kW Triton shower to replace, which is turning out to be more problematic than I thought :
2 people say I need a bigger cable than the 10mm cable already installed while 2 others say the existing cable is fine. I stopped in at a large B&Q yesterday and their bathroom advice guy says they always fit 10.5kw with a 10mm cable and mentioned section/paragraph/something 27 as the guidelines they follow.

i have a 45amp circuit breaker for the unit already

so what should I do ? Get retired or fit the unit with the existing cable ?

thanks in advance
 
A 10.5kW shower would (in principle) pull about 46A in current a 10mm² flat twin and earth cable is only rated for that level of current if the cable is clipped directly on the surface of a wall, buried in plaster in a wall or laid in contact with the inner plasterboard of an insulated stud wall.
If the cable is buried in insulation, in trunking or conduit then the cable is not rated for that load and you would need to use 16mm² cable (so long as it was not buried in insulation).
Strictly according to the regulations the 45A circuit breaker is also not sufficient and you would need a 50A breaker that would then prevent you using 10mm² cable unless it was only clipped direct (or in plaster).

The best solution here would be to return the 10.5kW shower and replace your shower with another 8.5kW shower.
 
A 10.5kW shower would (in principle) pull about 46A in current a 10mm² flat twin and earth cable is only rated for that level of current if the cable is clipped directly on the surface of a wall, buried in plaster in a wall or laid in contact with the inner plasterboard of an insulated stud wall.
If the cable is buried in insulation, in trunking or conduit then the cable is not rated for that load and you would need to use 16mm² cable (so long as it was not buried in insulation).
Strictly according to the regulations the 45A circuit breaker is also not sufficient and you would need a 50A breaker that would then prevent you using 10mm² cable unless it was only clipped direct (or in plaster).

The best solution here would be to return the 10.5kW shower and replace your shower with another 8.5kW shower.

You may well find that the "10.5kW" rating is quoted for a supply voltage of 240V. If so, the current drawn at 240V will be less than 45A (and even less at 230V), so a 45A breaker will be fine.

Provided that the cable isn't covered in loft insulation, I'd say that 10mm² will do the job.
 
Thanks for the replies guys.
Ive taken the less costly route of buying a 9.5kw shower unit - which thanks to the Tesco vouchers double value promo ended up costing nothing..... So hopefully the 10mm cable is sufficient now
 

Reply to 10.5 kW shower - advice/help required in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
726
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock