Yesterday smelt a weird smell of burning/melted plastic in my bathroom after some looking about realised was the shower pull cord opened it to the the incoming live insulation completely melted an charred and the pull cord terminal melted shower was installed about 3/4 years ago but recent board change by council(council house), I've done a cable calc and l got a Ib of 45.65 A so next suitable breaker 50A and got a 10mm t&e, currently on 6mm 40A breaker. Would you reckon this was the reason it had melted or due to other reason?
Ps have isolated removed switch and stopped using shower
depends on the installation method. 6mm method C is 47A.
It is the wrong size cable for a 10.5kw shower, and yes it really should be 10mm on a 50A mcb. but none of that would have melted the terminal at the pull switch. :)
It is method C comes up threw void under airing cupboard then clipped in airing cupboard only bout 3 or 4 metre run but then still being 47 A wouldn't it be 50a breaker required? And 10mm
no, In < Iz. so that the MCB trips before the cable is overloaded. so if Izis 47A, then a MCB below 47A In is selected.
you get a little warmth at the terminations in the switch due to load current. this leads to expansion/contraction leading to a slightly loose connection after time. this then starts to arc, burn, and before you know it here comes fireman sam with his hose.
To be honest I doubt that a 6mm cable would have melted on a 45/50 amp supply unless the cable was sub standard and there have been cases of that.
More likely the switch had melted due to
a) Loose connection
b) Moisture getting into it and shorting
c) Cheap and nasty accessory ( same as cable could have been)
d) Old accessory that was rated 45amp and finally broke down
the 40A breaker will protect the 6mm from overload. start off by replacing the switch for a good quality one, crabtree round ones have good reports. then with the shower going full heat, clamp the L core in the DB and see what it's drawing. i'll be surprised if it's > 40A.
It did get damaged, so no need to upgrade cable or breaker? And I was guna replace it with cooker type switch in airing cupboard and don't have the equipment to test only a apprentice
Reply to 10.5kw shower in the UK Electrical Forum area at ElectriciansForums.net
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Hi I recently purchased(aug18) a house built in 1963 and about an hour before bed I smelt a burning smell in the hallway. I looked around and...
So abit of a random one. But yesterday my Neighbor asked me if I'd be able to take a quick look at their shower as it had stopped working. I said...
Hi had a 45amp shower pull cord switch melt on me so replaced it with a 50amp one did it all correctly but no joy and the switch doesn't come on...