Hi,
I'm installing a 10.8 kw shower and looking at other forums everyone is saying 10mm is OK however i can't see how.
10800W/230V=47A
breaker size 50A
the only way it can be a 10mm is if its clipped direct with no insulation as it can take 64A however if it is any other reference then the rating is less than 50A.
so how is 10mm enough to carry the load?
what have i missed?
I'm installing a 10.8 kw shower and looking at other forums everyone is saying 10mm is OK however i can't see how.
10800W/230V=47A
breaker size 50A
the only way it can be a 10mm is if its clipped direct with no insulation as it can take 64A however if it is any other reference then the rating is less than 50A.
so how is 10mm enough to carry the load?
what have i missed?