Does anybody know the tripping times for a 100ma 100a rcd, x1 and x5 many thanks for your previous help earliar.......................;)
 
It depends on the bs number of the RCD
Bs 4293....@1x-200ms ...... if it incorporates a time delay it should trip within a range of 50% to 100% of the rated time delay plus 200ms.
Bs 61008....@1x-300ms.......... with time delay within the range of 130ms to 500ms.
But keep in mind that final circuits up to 32a on a TT are required to disconnect within 200ms with a fault of negligible impedance.

OSG chapter 11.
 

Reply to 100ma rcd tripping times please??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock