Hi all. Just to see your opinions on this.
Started work on a local authority housing job. Wiring showers in highflats.

The spec is 2 way rcd enclosure with 40a mcb and the other way blanked off.
We are to use 10mm tails into henleys. 25mm tails in use for cu and 100a main fuse.
I say we should be using 25 as its 100a cutout. But foreman says its ok as it wont pull more than 40a.

I would agree with him if it was a 40a stand alone rcbo only. But the extra way leaves it open for they 10mms to be overloaded.

Thoughts please
 
I would use maybe 16mm, no problem with sizes in this day an age being all modular, eg if it was an old 2 way wylex board, 45amp dp switch you would not get 16mm in let alone 25mm in the terminals.
 
I would say that when working on a local authority job to a specification then I would follow the spec unless there was something obviously dangerous


Sent from my iPad using Tapatalk
 
Whilst it is unlikely the spare way would be used for another 40A load you are never the less correct, the risk is there and it is placed there by the installer.
 
Agree with others, yes future proofing things is always a good practice but budgets and finances often dictate otherwise. as long as what you do complies and is safe then get on with it and move to the next one and the next one and the next one.
 
10mm tails are fine. 6mm would be adequate for the load.
If it's a 63A rcd then in theory any self respecting installer would not put more than 20A on the spare anyway.
If your concerned just put a max load label on the CU.


Sent from my iPhone using Tapatalk
 

Reply to 10mm DI tails in henleys in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
786
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Evening all. I have a question as I can’t get my head around something with solar PV I’m going to be working on a new build in a couple of...
Replies
9
Views
2K
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock