Afternoon all been a while since I've posted.


at today's job I noticed 10mm meter tails with 6mm bonding and although my first thoughts were tails should be min 16mm and bonding 10mm

so at the risk of sounding stupid I couldn't find the exact reason why this was wrong as the 10mm would take 61amps

could anyone clear this for me?
 
Bonding is under sized, though it probably complied at the time of design/construction.
Nothing wrong with the CSA of the tails as far as BS7671 is concerned, though they are probably not double insulated.
 
Last edited by a moderator:
PVC insulated and sheathed I think you'll find, often referred to as DI though, but not strictly correct. A bit like calling a vacuum cleaner a hoover....everyone knows what it means even if it's not strictly correct.
 
Whether a cable is described as being double insulated, has no bearing on whether it is or isn't as far as BS7671 is concerned.
What matters is whether the cable complies with the requirements.
As cables with insulation and sheaths, and cables with reinforced insulation satisfy the requirements for double insulation, such cables are deemed as being double insulated.

Risterd despite your obsessive compulsion to disagree with me at every opportunity, I suggest that if you do not like my use of the term 'double insulation' for cables that satisfy the requirements for double insulation, that rather than continue this childish sniping at me across various forums, you take this particular matter up with the JPEL 64 committee.
By all means continue chasing after me, if that floats your boat.
 
Last edited by a moderator:
Whether a cable is described as being double insulated, has no bearing on whether it is or isn't as far as BS7671 is concerned.
What matters is whether the cable complies with the requirements.
As cables with insulation and sheaths, and cables with reinforced insulation satisfy the requirements for double insulation, such cables are deemed as being double insulated.

Risterd despite your obsessive compulsion to disagree with me at every opportunity, I suggest that if you do not like my use of the term 'double insulation' for cables that satisfy the requirements for double insulation, that rather than continue this childish sniping at me across various forums, you take this particular matter up with the JPEL 64 committee.
By all means continue chasing after me, if that floats your boat.

girls,girls!
 
Afternoon all been a while since I've posted.


at today's job I noticed 10mm meter tails with 6mm bonding and although my first thoughts were tails should be min 16mm and bonding 10mm

so at the risk of sounding stupid I couldn't find the exact reason why this was wrong as the 10mm would take 61amps

could anyone clear this for me?

Why do you say minimum 16mm tails and 10mm bonding?
The minimum size for bonding is 6mm unless PME conditions apply.
There is no lower limit on tail size, other than the availability factor.


Sent from my iPad using Tapatalk
 
What matters is whether the cable complies with the requirements.
As cables with insulation and sheaths, and cables with reinforced insulation satisfy the requirements for double insulation, such cables are deemed as being double insulated.

.

Well if you want to be pedantic then technically speaking an insulated and sheathed cable may be considered to afford equivalent protection to DI subject to some stipulations (which I can't remember) rather than actually being deemed to be double insulated.

Plus reinforced insulation is a separate thing to DI, although the regulations consider them to be equivalent.
 

Reply to 10mm meter tails 60amp fuse 6mm bond in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
769
Hi I don't know if I should ask it here or the main electricians forum. It's about CU change and the work around it and the CU change will be done...
Replies
78
Views
11K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Hi all, This week while wiring a very old farmhouse for heaters I noticed the incoming cu tails were very long, around 20 metres from the fuse...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock