Why do you say minimum 16mm tails and 10mm bonding?
The minimum size for bonding is 6mm unless PME conditions apply.
There is no lower limit on tail size, other than the availability factor.


Sent from my iPad using Tapatalk

Do you not mean to say 'demand factor' or 'load factor'?
 
V/Ze= 766A

I=766
T=0.16
K=143 (not incorporated in a cable or bunched)

766x766=586756

586756x0.16=93880

square root of 93880=306

306/143=2.13mm for your main earthing conductor.

Taking reg 544.1.1 in to account the 6mm bonding conductor is adequate.

Edit: Based on a BS1361 fuse

Hi Lee or anybody else. Can you confirm what the T value of 0.16 relates to with this calculation?

Thanks
 
V/Ze= 766A

I=766
T=0.16
K=143 (not incorporated in a cable or bunched)

766x766=586756

586756x0.16=93880

square root of 93880=306

306/143=2.13mm for your main earthing conductor.

Taking reg 544.1.1 in to account the 6mm bonding conductor is adequate.

Edit: Based on a BS1361 fuse
Hi Lee or anybody else. Can you confirm what the T with value of 0.16 relates to here?

Thanks
 
The supply authority and utility provider will expect to see 16mm tails and therefore a 10.0mm bond is required to satisfy their requirements also. The regs and calculations can determine other values but to ensure you meet the minimum requirements of the energy supplier this is what I would install as a contractor.
 

Reply to 10mm meter tails 60amp fuse 6mm bond in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
785
Hi I don't know if I should ask it here or the main electricians forum. It's about CU change and the work around it and the CU change will be done...
Replies
78
Views
11K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Hi all, This week while wiring a very old farmhouse for heaters I noticed the incoming cu tails were very long, around 20 metres from the fuse...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock