EN61558 specifies a 25% duty cycle e.g. 5 minutes on and 15 minutes off for power tool transformer intermittent ratings. Since the copper loss is proportional to the square of the load current, and assuming the duty cycle to be approximately the reciprocal of the heat dissipation when under load, the intermittent rating will be approximately 1/(sqrt (0.25)) = 2 * continuous rating. So a 1.65kVA continuously rated transformer will offer a power tool intermittent (25% duty) rating of around 3.3 kVA. For those 5 minute periods it will deliver 30A and the wiring and OCPD needs to allow for this.