Installing a wall mounted transformer.

Single phase with 2 x 16 amp sockets

Input connections are 240v 220v 0v 10v

Output/secondary side 55v 0v 55v

Whay would the connections regarding the input/primary side live neutral earth.

The 10v is throwing me off
 
.
.



With the 10v (effectively -10v) you can get inputs of;

0v and 220v = 220v
10v and 220v = 230v
0v and 240v = 240v
10v and 140v = 250v

As per Brian, to trim the 55 0 55 to 110v, depending on the available input voltage.
 
What they ^^ said, to accommodate various mains voltages. Note that the tapping should be chosen on the basis of the actual mains voltage, not adjusted to put the output voltage 'right' when off load, because the voltage will fall by the regulation percentage once full load is applied. For example, on 230V mains you might find the output closer to 55-0-55 using the 240+0 taps rather than 220+10, if measured off load. But on load the voltage would fall, possibly out of spec. If the mains is 230V use 220+10.
 
All mains voltage is declared as 230 volts, and a few years ago it was declared as 240 volts, but no actual changes were made.
Definitely measure the output voltage under load, but don't assume that 220 + 10 are the correct taps, just because the DNO say so.
My own supplies are normally around the 245 volt area.
 
I also normally see 240V+. The DNOs like to keep it as high as they can (without going over the upper limit of course) as that minimises I2R losses and maximises the capacity of the network. But things have changed somewhat with the level of embedded generation (mostly solar PV) and I suspect quite a few final substation taps have had to be changed where changed/reversed power flows have resulted in higher end user voltages (probably coming to light as a result of the owners of the new PV installs complaining that their inverters trip out on very sunny days).
 

Reply to 110v transformer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I want to benefit from your experience regarding a delta secondary service. We are upgrading an electrical vault. On the primary side, we are...
Replies
0
Views
283
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Ok, i am new in this forum I am looking for some enlightenment. Today I got a call from my boss, which is now in Venezuela and he is connecting a...
Replies
4
Views
1K
Hi all, No electronic knowledge here. The plug/transformer of a led lightstring is fried. Now I am trying to find a replacement on Aliexpress...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock