This is one of those jobs that has the possibility / probability of ending up in a lot of finger pointing
There are some questions that need to be asked like when it comes to the EIC who is going to put their name on the design, when the installation has issues due to exceeding the volt drop limits who will take the blame
my question was not how to calculate voltage drop but for suggestions on how to terminate from one size to the other
I think without people posting concerns about the volt drop and size of cable to be used it may be seen as they are accepting the design of others is compliant while they are offering advice on the the question you asked
but there are options & maybe I've not considered them all
IMO there are options not least walking away from a job with a recipe that has all the ingredients of an acrimonious ending because of the issues that this thread has highlighted a simple one a few years down the line what happens if the property is sold and the EICR done as part of the sale is found unsatisfactory You can do many excellent jobs that no one will hear about but the one that goes wrong everyone will hear about it
 
£40K was the cost for mains supply to the source. The client was told that he could save money & build a meter box on the edge of the property & install his own supply from that source. This was suggested by REC. This is not an install that I relish...
Were the cable calculations done by the DNO?

If so it might be reasonable to assume the system is what they would have done had the cut-out been installed at the property so your end of sub-main voltage remains within ESQCR specifications.
 
Get the customer to get a quote from DNO to install up to where you really want the incoming cutout. If the customer is willing to dig the trench you may find there is not much in it cost wise and it will be done correctly.
 

Reply to 120mm to 25mm connection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
768
I’ve got a job to quote for turning 1 big flat into 2 smaller flats. The DNO are looking at installing new meters in the communal area. I need to...
Replies
3
Views
1K
Evening, I've been asked to install a supply to a sprinkler system in a new installation that must be separate to the building electrical...
Replies
2
Views
554

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock