Hi, Ive got an upcoming job to determine the cause of a BS88 fuse tripping in a switched fuse unit that powers a 125A consumer unit yet none of the MCB's trip, Just the one cartridge fuse.

What is a concern about this site is that the old fused switch unit is 63A, yet it is feeding a 125A consumer unit. This is apparently a recent install too. The consumer unit is used for 4 ring circuits rated at 32A.

Surely this shouldnt have been signed off on the installation certificate as the switched unit is under rated?

Any help is greatly appreciated, Thank you
 
So you need to discover whether the 63A fuse is blowing due to fault or overload. It sounds like overload, but you might have to clamp the circuit to prove that, if it is not obvious from the connected load.

You can't say that the switch-fuse is under-rated without knowing what the load is. If there are ten 200W computer loads plugged into each ring, the four rings might be completely justified and well utilised, with a total load of only 35A and the fuse is perfectly adequate. The 125A rating of the consumer unit is neither here nor there.
 
It would be bad practice if the original installation exceeded the 63A fuse rating, but before laying the blame at the original sparky who signed off, it might be worth checking to see what has changed (if anything) since then in terms of how it is used.

Having 4 RFC at 32A does not imply they were planned to be used to that load, it might have been for fault tolerance or some other reason.

But equally it might be the design expected close to 100A but for some reason or another the supply was not uprated to suit. Is this a domestic set-up? Has someone added a 10kW shower or EV charger (in addition to several electric heaters in normal use)?
 

Reply to 125A consumer unit powered by 63A Switched BS88 Fused Unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi, The `power went out throughout the house this afternoon but only to the sockets, the lighting circuits are all fine. I went to the consumer...
Replies
9
Views
1K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock