Discuss 125A D Type MCB keeps tripping on a heater element circuit, i changed the MCBs to 100A C Type and it has not tripped again. I dont know why? in the Electrical Engineering Chat area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:  American Electrical Advice Forum

I changed 3 x 125A fuses for 3 x 125A D type MCBs (ABB). They held for a day and then two started tripping, we didn't have any spare 125A, so we fitted 100A C type and the issue has disappeared, can anyone shed any light on this for me please?
 
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members

Pete999

-
Arms
Esteemed
Is this a TP and N circuit and are you using 3 x SP MCBs? Does the heater bank require a N or is it a balanced load, maybe try a TP MCB
 

pc1966

Arms
Esteemed
There is no sensible reason for a 100A C-curve MCB to resist tripping that a 125A D-curve MCB would respond to, short of one or the other being faulty (125/D too sensitive, 100/C not responding as it should).

I would suspect an unfortunate timing of faults behind this. Something downstream with medium/high MCBs and a fault would also trip a MCB upstream (but probably not a fuse, or a suitably configured MCCB) so you should check for that sort of thing.

Also Pete999 has a very important point - in a 3-phase system you really don't want to lose a phase if any loads are 3-phase (motors, etc) so you ought to be looking at linked 3-pole breakers.

Yes, you had 3 separate fuses before. But they ought to have been coordinated with downstream breakers so you get selective and so very little chance of a fuse going on a minor fault.
Post automatically merged:

Another though is the 125A D-curve had a poor connection and was heating up causing it to trip prematurely, and a change fixed that. But I suspect you would have seen signs of thermal stress there (or found it hot shortly after power off when replacing).
 
Last edited:

James

-
Mentor
Arms
Supporter
Esteemed
I think the main point here, is not why some fuses or breakers are tripping or blowing quicker than others.

posts 2,3,4 & 5 are all trying to point you in the direction of finding the fault.

I would suggest that you stop straying from the obvious fault (fuses of different types, characteristics and ratings are all blowing)

FIND THE UNDERLYING FAULT and fix it.
 

PEG

-
Mentor
Arms
Esteemed
Maybe it's an exam question type scenario? .....and we've been getting excited,too early?
:)
 

pc1966

Arms
Esteemed
72A on phase 1 and 3 and 82A on phase 2, there are 21 elements on the circuit totaling 60kw. This is all correct, we are now getting excessive heat on the 35mm cables.
Are they aluminium 35mm? I would be very surprised to see copper 35mm overheating at 82A!

Even Al would be roughly 23mm Cu equivalent and ought to cope with that sort of current.
 