GBDamo

-
Esteemed
Arms
Reaction score
3,010
Was called out to a wall heater not working, took FCU off and both L and N supply cables had snapped off. This is a spur off a ring. I have not tested the ring as cannot isolate but all plugged in equipment is performing normally.

Voltage on the exposed ends L-N was 124V, L-E 238V.

My thoughts are loose connection at the point it spurs of the ring or damaged cable.

Any other theories?

I have two hours this evening to find the fault and make safe, can't turn the power off until 18:00.

Ta in advance
 
You may be picking up induced voltage if you are using a digital multimeter. You could see something like those strange voltages if the N is disconnected elsewhere. Either test L-N under load, or use a proper voltage tester.
 
You may be picking up induced voltage if you are using a digital multimeter. You could see something like those strange voltages if the N is disconnected elsewhere. Either test L-N under load, or use a proper voltage tester.
My proper voltage tester is in a ceiling in Blackpool, left it there this morning so using my Fluke 375FC clamp meter with probes to test for voltage.

When I can get in and isolate I can look for where the spur originates and get my MFT on the job.
 
Well what a lash up.

Turned out to be two 2.5 radials, no continuity on L,N or earth so unlikely to be a broken ring, on a 32A RCBO, traced one to the heater and no other points and couldn't find the second.

One neutral was sat in the RCBO terminal but not tight.

Found about half a dozen other C2s on the three circuits I tested so disconnected those I could and left.

Will be back another night.
 
Hum ........ you have no rights to leave such issues disconnected.
Yes I do, i have the trust of the customer not to leave them without critical equipment while leaving the site as safe as possible, these were non critical circuits.

Obviously I wouldn't have done this with 90 year old Doris leaving her with no heating and hot water, be more inclined to stay a few more hours to resolve.
 
Last time I had those figures someone had connected neutral to earth and earth to neutral on a lighting circuit. It was a TN-C-S supply.
 

Reply to 125V L-N on cable at FCU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello, you all helped me out recently when we had a water leak (mostly in kitchen ceiling), and my landlord's contractor was saying the household...
Replies
7
Views
2K
B
Have just had a neighbour knock on my door and ask me to go round and look at a shed power supply he has attempted to install. Layout is as...
Replies
37
Views
3K
Eh up :) I don't do EICRs - not enough experience - but the things I see on some reports done by others really dismay me. Perhaps some of my...
Replies
21
Views
5K
D
Hey all, I'm just starting to dabble in my own testing just to gain experience, while awaiting a course start. Some questions I'm not sure...
Replies
12
Views
2K
vectraj
V

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock