Hi all, good afternoon.
New on here, so here goes!

Quick question and some advice really!

I have a 12KW three phase immersion heater installed into a hot water cylinder (for commercial premises).
The immersion heater enables and disables via an on site building management system so therefore the immersion heater enables via a Schneider (3ph) ICT 25A 400v contactor. Complete with 230v coil.

The building in question (their maintenance man) is explaining to me that he thinks the contactor is 'under rated' as the 12KW immersion heater will be drawing more load?? Also he seems to think the contactor is changed every 12 months or so??

above the contactor there is a Schneider (3ph) C60HB B20 415v MCB installed.

What kind of load 'potentially' could a 12KW three phase immersion draw? Is it simple ohms law?

12000 watts (12KW) / 400v = 30 amps or is there (back to my college days) a route3 equation in there somewhere + a power factor? I feel a clip on clamp meter coming on soon!

Feedback appreciated

Thanks
 
Right equation, wrong voltage I think.
Check the rating of the immersion heater, it's almost certainly going to be rated 12KW at 415V not 400V

Do you know why the contactor is being regularly replaced? Is it the coil burning out or the actual contacts at fault?
 
The question of why the contactor is being changed is very relevant.

From a design point of view the contactor and circuit breaker are rated OK for the load and 16-17 A is about right for the load.
I cannot think of a contactor type that should not be able to handle a pure resistive load, though the contacts could be wearing out if it is switched on and off a lot.
 
Rich/Dave many thanks.

I will confirm with Santon the immersion heater people to see if its 12KW at 415v or 400v.

Also you make a good point regards the coil burning out and not the contacts - When I attend I will check this.

Could you work it the other way also? Just curious! so -

12÷3=4

12kw ÷ by 3 phases = 4kw. 4kw is 4000 watts

Amps = 4000/(1.73x415)=5.57amps per phase

5.57 x 3 = 16.71 Total?
 
Rich/Dave many thanks.

I will confirm with Santon the immersion heater people to see if its 12KW at 415v or 400v.

Also you make a good point regards the coil burning out and not the contacts - When I attend I will check this.

Could you work it the other way also? Just curious! so -

12÷3=4

12kw ÷ by 3 phases = 4kw. 4kw is 4000 watts

Amps = 4000/(1.73x415)=5.57amps per phase

5.57 x 3 = 16.71 Total?

Nope, approx;
4000 / 240 = still 17amp per phase.

Typical real world clamped current on a 12kw is 16.5 amp per phase, I've checked quite a few over the years.

And they'll be Star connected and 415v rated
 
Would they not be 240v rated elements if connected in star?
sv

Because you can get 115V, 240V, 380V, 415V, 440V, 550V and 660V elements. They’re just the ones I’ve come across over the years.

Never assume anything, check the rating plate and manufacturer’s destructions.

I was called to a product tank heater that reportedly wasn’t working. It was supposed to be 30KW, the product was turning to sludge because it was cold. Whoever connected the heater assumed it was star and connected it as such, it was only giving 9.2KW.
 
it's 400 because the frogs can't do sums with numbers that don't end in 00.
 
In either case, it's the 12kW that determines the line current.
The three-phase voltage in this country is 400V - at least nominally.
Harmonisation is wonderful...................:(

That’s strange, I recall a conversation on a site outside the UK where you backed me on UK voltage levels ;-)

The IET and EU forgot to tell UKPN, if they had they would get a resounding **** ***!

It’s not feasible and never will be to change from 433/250V. What annoys me are calculations based on a purely fictitious value. They are inherently 7.6% inaccurate.

I’m just waiting for the Belgians to step in with 380/220V as the new harmonised voltage.
 
400V for example.

It’s about time the IET got their collective heads out of their collective arses and accepted the fact the supply voltage isn’t going to change.

I’ve said it many times before, what is the point of basing calculations on an erroneous value.
It’s like the state of Indiana decreeing in 1879 the value of π was to be 4.

UKPN own the bat and ball, they make the rules to suit themselves. Its just like school ;-0

Role on the 18[SUP]th[/SUP] edition, it will be 380V by then. (I’ll be dead with any luck.)
 
tonyt, you and me both can't die for a long time yet. still too many people to annoy.
 
400V for example.

It’s about time the IET got their collective heads out of their collective arses and accepted the fact the supply voltage isn’t going to change.
I have made that very point several times here and elsewhere which is why I called it a fudge. Did you miss that point?

Post #14 from me:

It's a fudge. And not a very good one at that.
 

Reply to 12KW three phase immersion heater in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Evening all, I've got an upcoming project.... looking for info on selectivity on some submains. currently the property in question has 2 100A...
Replies
17
Views
3K
Hi all! My current dilemma: What was three small offices is now one large one. So I have x3 DB's feeding x3 electric heaters on their own timers...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock