I’ve just had a ‘robust exchange of views’ :) with a visiting engineer about the 16A sockets in my workshop. These, together with local 13A sockets, are run from radials in 2.5mm, protected by 20A RCBOs.

I say it’s fine to have say a couple of 16A interlocked sockets, and lots of 13A doubles on each radial.

See pictures below: All the sockets in each picture are on the same individual radial (Ignore the 3P socket and the drill supply).

The visitor insisted you must have a separate circuit for 16A sockets, protected at 16A.

I say that’s rubbish, as the protection in this case is rated to the cable CCA and length, and 20A max is fine for 16A sockets as 16A plugs are not fitted to equipment which draws more than this.

All is under the supervision of trained personnel. Care is taken with load balancing as the supply in this remote building is limited to 20A per phase anyway.

Who is right?

DSC_0767.JPG

DSC_0768.JPG
 
I’ve just had a ‘robust exchange of views’ :) with a visiting engineer about the 16A sockets in my workshop. These, together with local 13A sockets, are run from radials in 2.5mm, protected by 20A RCBOs.

I say it’s fine to have say a couple of 16A interlocked sockets, and lots of 13A doubles on each radial.

See pictures below: All the sockets in each picture are on the same individual radial (Ignore the 3P socket and the drill supply).

The visitor insisted you must have a separate circuit for 16A sockets, protected at 16A.

I say that’s rubbish, as the protection in this case is rated to the cable CCA and length, and 20A max is fine for 16A sockets as 16A plugs are not fitted to equipment which draws more than this.

All is under the supervision of trained personnel. Care is taken with load balancing as the supply in this remote building is limited to 20A per phase anyway.

Who is right?

View attachment 56117

View attachment 56118
Stick them on a 4mm2 Radial with 32A CB
 
Stick them on a 4mm2 Radial with 32A CB
Thanks, but 16A skts on 32A? Naa. Feels wrong. Too much opportunity for it to end badly.

Plus this remote building has a limited supply, it's protected at 32A upstream, so I limit local breakers to 20A for (hopefully) a bit of discrimination.
 
The purpose of the over current protective device is to protect the installation from overload. If it's all wired in 2.5mm cable, then a 20A device will achieve this, so whilst it's not ideal, I can't think of any regulation it breaks.
 
The OSG reckons that unlimited 16A sockets on a 20A radial is fine. Appx H, H3.

Whether this is at odds with reg 512.1.2 I'm not entirely sure
 
It isn't strictly correct as you haven't provided protection against overcurrent (overload), whilst the cable is OK, the socket outlet is rated at 16A not 20A and is therefore unprotected.
A 16A socket outlet is unlike a 13A version because it does not have a fuse - the 13A outlet cannot be overloaded as is fused in the plug, the 16A does not.
It is normal practice though.
 
It isn't strictly correct as you haven't provided protection against overcurrent (overload), whilst the cable is OK, the socket outlet is rated at 16A not 20A and is therefore unprotected.
A 16A socket outlet is unlike a 13A version because it does not have a fuse - the 13A outlet cannot be overloaded as is fused in the plug, the 16A does not.
Yes, regardless of what the regs say, that's fair, but 16A plugs tend to be fitted to equipment incapable of drawing more than 16A, and there's leeway in the specs, especially for intermittent loads, and I only fit quality plugs and sockets.
A 13A socket can most certainly be overloaded (in theory): by plugging two 3kW loads into the same double socket, which is rated at only 20A overall. No one does that though, as it would be silly :)
 
As above, it's permissible to have more than one 16A BS EN 60309 socket-outlet protected by a 20A device. However they shouldn't really be sharing a circuit with BS 1363 socket-outlets (although admittedly not dangerous).
 
As above, it's permissible to have more than one 16A BS EN 60309 socket-outlet protected by a 20A device. However they shouldn't really be sharing a circuit with BS 1363 socket-outlets (although admittedly not dangerous).
Thanks. I admit it does feel slightly wrong, but I could think of no electrical reason why it's not OK. I wanted to have multiple radials and was running out of ways on the DB. I thought this semi-lash-up was better than keeping 16A and 13A separate but then having too great a floor area served by each circuit.
Any anything is better than encouraging the use (by clients) of these horrible things:
PL14282-40.jpg
 
Yes, regardless of what the regs say, that's fair, but 16A plugs tend to be fitted to equipment incapable of drawing more than 16A, and there's leeway in the specs, especially for intermittent loads, and I only fit quality plugs and sockets.
A 13A socket can most certainly be overloaded (in theory): by plugging two 3kW loads into the same double socket, which is rated at only 20A overall. No one does that though, as it would be silly :)

In your own workshop, I wouldn't be too worried either way, on some sites though I would have each fed from single 16A MCB/RCBO - I have seen too many 32A welders connected via 16A plugs ('nice' 16A plug - 32A socket adaptor lead), but outwith welding shops and the like, I would consider it OK even though technically there's a discrepancy.
 
Stick them on a 4mm2 Radial with 32A CB

That is terrible advice, the maximum ocpd for a 16A socket is 20A.
[automerge]1583175755[/automerge]
As above, it's permissible to have more than one 16A BS EN 60309 socket-outlet protected by a 20A device. However they shouldn't really be sharing a circuit with BS 1363 socket-outlets (although admittedly not dangerous).

Why shouldn't they be on the same circuit?

I'm curious as we regularly install circuits with a 13A, 15A and 16A outlet all on the same circuit and I've never yet seen a Regulation preventing this, plus the NICEIC assessor has never had an issue with it.
[automerge]1583175925[/automerge]
Yup, why does this item even exist? :)

(I do admit to owning one though, used only occasionally and with discretion :) )

It exists to allow something with a 32A plug to be connected to a 16A socket, we've got a few and use them all of the time.
In fact we've got adaptors from ever size of blue and red commando up to the next size in our stock.
[automerge]1583175970[/automerge]
Any anything is better than encouraging the use (by clients) of these horrible things:
View attachment 56122

What's wrong with a 13-16 adaptor?
 
Last edited:
Nothing wrong at all. Very useful for testing equipment if you have only got a 13A socket available. And there's a 13A fuse in the plug.
 
That is terrible advice, the maximum ocpd for a 16A socket is 20A.
[automerge]1583175755[/automerge]


Why shouldn't they be on the same circuit?

I'm curious as we regularly install circuits with a 13A, 15A and 16A outlet all on the same circuit and I've never yet seen a Regulation preventing this, plus the NICEIC assessor has never had an issue with it.
[automerge]1583175925[/automerge]


It exists to allow something with a 32A plug to be connected to a 16A socket, we've got a few and use them all of the time.
In fact we've got adaptors from ever size of blue and red commando up to the next size in our stock.
[automerge]1583175970[/automerge]


What's wrong with a 13-16 adaptor?
There are 13 Amp sso involved 4mm2 32 Amp no worries, wire the 16Amp sso on their own 20Amp OCPD
 
Your post certainly didn't make that clear.

So what you're suggesting here is to remove this perfectly compliant installation and install new circuits?
Yep I am 4mm2 for the 13Aand 2.5 for 16A 32 and 20 OCPDs respectively
 
... My biggest concern is how clean and tidy that workshop is, that can't be healthy.
Ha Ha! It was not always thus.

Now I'm semi-retired I rent the workshop out as a sideline. So it has to be nice and tidy, to aerospace/military standards: Mop the floor, polish the bloody sockets, clean the tops of the doors and so on ...

I used to have six work tables, all of which gradually got covered with works-in-progress in a total mess and there was never anywhere to put anything down. So to solve this, I didn't get rid of the works-in-progress, I got rid of the tables. Reduced to two. So I now have to put stuff away properly, in nicely-labelled boxes in the tool room.

Which means, of course, that I can no longer find anything! :)
 

Reply to 13A and 16A sockets on the same 20A radial. OK or not? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Got an issue with gym equipment. ( I keep telling my wife I’m going to the gym, but she doesn’t believe me!) The gym owner says the circuit for...
Replies
13
Views
2K
Hello everyone, Back again after receiving great advice for the bathroom a few months back. This time I'm making a mess in the kitchen. We have...
Replies
1
Views
1K
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Replies
18
Views
3K
  • Locked
So, a flat 6 floors and above needs an AFDD on each socket circuit. At up to £150 each it is going to be an expensive undertaking if there are...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock