Just a quick one, all my books are in college.

Is it acceptable and up to current 17th to use 16A on a radial. Wired in 2.5 T&E, short run (8M) with 3 sockets.
I have used 20A in all other flats (6 of), but got to the last 2 flats and ran out of 20's, so my colleague put 16's in. I'm 99.9% certain it is 20's, but is there anything wrong with downgrading.

Just to settle my little dispute.

Cheers Guys
 
K

kung

  • Thread Starter Thread Starter
  • #2
Id stick with 20 for radial and 32 for ring as sockets you cant be sure what they will supply.
Regards
Kung.
 
S

Spudnik

  • Thread Starter Thread Starter
  • #3
Agree with that^^

Also, why not just change the MCB's at the suppliers for the correct ones??
 
G

Guest123

  • Thread Starter Thread Starter
  • #4
All having a 16A MCB means is that the circuit will not be able to supply as much equipment as a 20A. Nowt wrong wi that but like the lads have said a 2.5mm radial will be more than happy on a 20A so I would swap them out also, gives the client a bit more scope.;)
 
D

daver

  • Thread Starter Thread Starter
  • #5
Thanks guys.

I knew I was right with the 20, but he is not wrong with 16 either under current regs.

He is a top guy at 74, no 17th edition but a fantastic mentor. I know what it will have been.

"Lunch break and a power nap, more important than going to supplier to change them"

Dave
 