Hi Guys,

Firstly, this is my own project and I have no 3ph supply in my own unit and have to take a supply from neighbors unit who has an old 3ph rewireable board with plenty of spare spaces.

I cant upgrade neighbors board and have to run a cable 35- 45m to supply a 18kw heater and fans.

My question is what size fuses do I need ??

The total current works out to be 43 amps with a 3.3% volt drop.

This gives me a minimum cable size of 6mm 4 core swa.

The question is . . . . . Do I try to source 45a fuse wire to cover the total current load or is the total current (43a) divided by the 3 phases making the fuse sizes smaller ???

Appreciate all your suggestions.
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members

telectrix

-
Mentor
Arms
Esteemed
is the heater and fans single phase or 3 phase?
 
E

Eric-George

  • Thread Starter Thread Starter
  • #4
Not sure where you got that 43amps from as an 18kw load over 3 phase would be 26amps per phase
Malcolm, you may have just answered my question. I got the 43a from dividing power by voltage (18000 / 410). I'm sure there a square root of 3in the calculation that I've missed?

43/ sqrt 3 (1.73) = 26 !!

Telectrix - Fans and heater are all 1 unit with 3 ph supply.
 

telectrix

-
Mentor
Arms
Esteemed
think the way forward is to split the tails to the neighbour's DB, install a 40A 3 phase MCB to feed your installation, add a meter if required so neighbour can charge for what you use. 6mm SWA if it meets VD limits beats 3 rusty nails in his DB.
 
Might just get away with 4mm as it's 3 phase Tel, but it's tight at 45mts so yes I would go 6mm
 