Discuss 18kw heater - 45m cable run - 3 phase - rewireable fuses. . . . Fuse size ???? in the UK Electrical Forum area at ElectriciansForums.net

E

Eric-George

Hi Guys,

Firstly, this is my own project and I have no 3ph supply in my own unit and have to take a supply from neighbors unit who has an old 3ph rewireable board with plenty of spare spaces.

I cant upgrade neighbors board and have to run a cable 35- 45m to supply a 18kw heater and fans.

My question is what size fuses do I need ??

The total current works out to be 43 amps with a 3.3% volt drop.

This gives me a minimum cable size of 6mm 4 core swa.

The question is . . . . . Do I try to source 45a fuse wire to cover the total current load or is the total current (43a) divided by the 3 phases making the fuse sizes smaller ???

Appreciate all your suggestions.
 
is the heater and fans single phase or 3 phase?
 
Not sure where you got that 43amps from as an 18kw load over 3 phase would be 26amps per phase

Malcolm, you may have just answered my question. I got the 43a from dividing power by voltage (18000 / 410). I'm sure there a square root of 3in the calculation that I've missed?

43/ sqrt 3 (1.73) = 26 !!

Telectrix - Fans and heater are all 1 unit with 3 ph supply.
 
think the way forward is to split the tails to the neighbour's DB, install a 40A 3 phase MCB to feed your installation, add a meter if required so neighbour can charge for what you use. 6mm SWA if it meets VD limits beats 3 rusty nails in his DB.
 

Reply to 18kw heater - 45m cable run - 3 phase - rewireable fuses. . . . Fuse size ???? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
814
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
965
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock