Hello all.

Quick question: Are 17th reg 3rd amendment metal consumer units compliant with 18th edition regs?

eg Hager VML716RKO

Many thanks (Newbie)
 
Aico 3000 Range
This official sponsor may provide discounts for members

SparkyChick

Mod
Mentor
Arms
Esteemed
And of course, don't forget you may need to accommodate SPDs and if the client goes for them... AFDDs (which may mean using two boards instead of one :D )
 

Andy78

-
Mentor
Arms
Esteemed
and the long answer is.......... ?
.......Possibly
 
In a nutshell, if you have 100amp cut out and 63amp rccb - don't overload it with mcbs that exceed the sum of 63amps. Use rcbos for the big circuits.
 
D

Deleted member 26818

Is it just Tool Station selling off 17th edition CUs cheap?
 

spark 68

-
Arms
Esteemed
If you look at the thread SC referred to above ^^^^ and read that reg (536.4.202) properly it is the design current for that RCD that needs to comply not the size of the company fuse etc, etc, , the last paragraph of that reg states manufacturers instructions should be followed, however in the same regs book, or at least in the 17th amd 3 book only states that manufacturers instructions should be taken account of.
 

Zdb

-
Probably best to supply full RCBO boards (with SPD) unless you can guarantee that your RCDs will be subjected to less than 9mA of earth leakage.
 

spark 68

-
Arms
Esteemed
Unlikely to hit 9mA in a domestic environment, besides which if you hit 10mA on a given circuit you are then into HI earthing, we hit this on office installs quite frequently where a lot of computers are installed.

Edit: 30mA RCDs tend not to trip until circa 22mA mark, @ 15mA they should not trip either.
 

mattg4321

-
Arms
Esteemed
Seen the price of the 100A RCCB's!

Doubles the price of most consumer units. Bet we won't be seeing many of them being fitted. Are they actually needed? Seems like the manufacturers trying to pull a fast one to me.
 

spark 68

-
Arms
Esteemed
Read Reg 536.4.202 again, and you will see it is the design current Ib that needs to be complied with, which is what most of us have always done anyway.
As said manufacturers instructions should be taken account of, not followed blindly.

Ps. Spin London was correct too it is also the ICn that is also important,
 
Last edited:
O

Octopus

Seems like the manufacturers trying to pull a fast one to me.
Hit, nail and head...........

If anybody thinks that they need to make sure that each RCD value is equal to or less than the main fuse they are being mislead.

Take this another step and you shouldn't have the sum of the MCB's or RCBO's exceeding the DNO fuse ............. which is madness.
 

Zdb

-
Unlikely to hit 9mA in a domestic environment, besides which if you hit 10mA on a given circuit you are then into HI earthing, we hit this on office installs quite frequently where a lot of computers are installed.

Edit: 30mA RCDs tend not to trip until circa 22mA mark, @ 15mA they should not trip either.
Screenshot_20190131-074222_Drive.jpg

TBH I'm not sure what the average leakage per RCD is for a typical split load domestic board as I don't do a lot of domestic. I would still recommend full RCBO though for a number of reasons.
 

spark 68

-
Arms
Esteemed
Oh I don't disagree, a full RCBO board is always nice to have if the customer will go for it, however they should always have been DP, or at least SPSN from the get go for obvious reasons.
 
T

Toneyz

I understand that Hager is going to install 100A as standard in the split boards you watch the assessors pulling us up on it.
 

Ian1981

-
Mentor
Arms
Esteemed
Historically we have used diversity of the final circuits to ensure that the rccb is not overloaded.
Now it seems we can not rely solely upon diversity of the final circuits downstream of the rccb and overload protection must be ensured by other means like having the upfront ocpd rated lower or equal to the rccb and main switch or ensure that the final circuits added are not greater than the rccb and ensuing manufacturers instructions are complied with.
I know with Hager they have taken the approach of fitting 2x 100amp rccb’s (Also now type A) in their dual rcd consumer units so obviously they intend to ensure that their rccb’s are not overloaded and have defaulted to use 100amp devices.
This is certainly the guidance also given by my companies scheme provider.
 

spark 68

-
Arms
Esteemed
Which reg states that though Ian ? 536.4.202 doesn't as far as I read it, Hagar is only one manufacturer out of many.
I normally take what you have to say seriously as you are one of the few that happens to know what you are talking about.

I had a look at the corrigendum for the 18th (yes mistakes again!) and nothing was mentioned wrt to this.
 

Wilko

-
Arms
Esteemed
I think it's the last para of that reg that's the killer, where they state " OCPD rating shall be selected in accord with manufacturer's instructions" . Rightly or wrongly, Hager has jumped in with both feet.
 

spark 68

-
Arms
Esteemed
Yes I know, however the same regs also state manufacturers instructions shall only be taken account of ;) they cannot have it both ways. don't you just love the IET :)
 

spark 68

-
Arms
Esteemed
And another thing the RCD is not a OCPD so as long as you stick below its design current Ina things should be fine, and no you cannot just add the breakers up as that would have a massive knock on effect wrt to diversity, The effing IET don't there ar*e from their elbow.
CIBSE should take over at least they seem to know what they are doing. :)
 

Ian1981

-
Mentor
Arms
Esteemed
536.4.202 states that overload protection shall not be solely based on the use of diversity factors of the downstream circuits.

536.4.3.2 states that rccb’s and switches to BSEN 60947-3 do not provide protection against overload therefore they shall be protected by an over current protective device
 

Ian1981

-
Mentor
Arms
Esteemed
The key sentence is that we can’t rely solely upon diversity of the final circuits and that manufacturers instructions are followed.
Given that Hager have jumped in and defaulted to using 100amp devices , my interpretation is that we must ensure the rccb is protected by not relying on the diversity factor
 

Ian1981

-
Mentor
Arms
Esteemed
BD6C804E-FAB3-494D-A807-5DEDDE0D2CF4.png 9DA728D6-F0AB-43A3-B154-B7642846A797.png BA885AE4-C447-4CA7-AC87-A5E5BE7458B2.png F8A2CB59-71B5-4A8C-AA75-14033F44DFE2.png
Sorry the pictures aren’t in order
 

spark 68

-
Arms
Esteemed
Are you telling me that say 3X 32A breakers plus a few 6A for ligting are going to exceed the 100A mains switch not to mention the absolute max of a 100A BS1361 type 2 incoming fuse ?
 

Ian1981

-
Mentor
Arms
Esteemed
Are you telling me that say 3X 32A breakers plus a few 6A for ligting are going to exceed the 100A mains switch not to mention the absolute max of a 100A BS1361 type 2 incoming fuse ?
No however Jpel/64 or Beama who are on the panels aren’t they are tell us yes?
As if a domestic installation will ever exceed say 80 amps or even 63 amps depending on size and the likes of heavy loads like showers.
I think the fact the potential could be there to cause overload is the driving factor to the regulation(s)
 
Last edited:

spark 68

-
Arms
Esteemed
As I said, we always had to design around a split load board, ie. we divided the circuits up and tried to load split anyway, just the regs never explicitly said we should, although this was common? sense to anyone sparking professionally.
 