Hi guys,I am currently revising for the 18th Edition exam a week on Friday and have come across a practice question that I cannot find any reference to in the BBB.
Here is the question they ask:-
If a fault occurs in the HV system,and a magnitude of fault voltage of 430 volts occurs between exposed conductive parts and earth on the LV installation.What is the maximum tolerable duration of the fault?

The answer is evidently 300ms.

I cannot find where they get this info from?
Any guidance would be most helpful.
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members

Charlie_

-
Arms
Sounds like they have got some questions mixed up..
if this was a game of jeopardy my answer would be...
When testing RCBOs to bs en 61009.
With a leakage current flowing equivalent to 100% of the rcd tripping current, what is the maximum disconnection time?
 