Just carrying out a EICR . Lightning circuit has a separate what looks to be 1mm single around all points. This has no mechanical protection so should be 4mm. Coding this has a C3. installation is still safe for continued use. Bit I’m struggling with is what section the C3 should fall under. If any? Any help?
 
Is it a single or a sheathed single? In the 1970s it was fairly common to use sheathed singles, the line one having an earth conductor, sort of 'single and earth'.
 
Just carrying out a EICR . Lightning circuit has a separate what looks to be 1mm single around all points. This has no mechanical protection so should be 4mm. Coding this has a C3. installation is still safe for continued use. Bit I’m struggling with is what section the C3 should fall under. If any? Any help?
When you state that "this has no mechanical protection so should be 4mm" (squared) do you mean that this is the cpc? If it is a live conductor then regardless of cross-sectional area it is not permitted to be lacking mechanical protection, e.g. a sheath. A non-sheathed cable used as a protective conductor must have a minimum cross-sectional area of 4mm^2 if not in containment etc.
[automerge]1579620806[/automerge]
Is it a single or a sheathed single? In the 1970s it was fairly common to use sheathed singles, the line one having an earth conductor, sort of 'single and earth'.
They're still common here. Although brown isn't necessarily brown & Earth. You can get PVC/PVC brown (no cpc) as well. And you can also get blue & Earth as well as PVC/PVC blue.
 
it’s single red with sheath, single black with sheath. Then a 1mm cpc solid green around all the accessories. The spec here for councils is still to wire in singles and cpc sheathed Both live and neutral must contain the cpc. In wholesalers we just ask for singles and earth.
 
it’s single red with sheath, single black with sheath. Then a 1mm cpc solid green around all the accessories. The spec here for councils is still to wire in singles and cpc sheathed Both live and neutral must contain the cpc. In wholesalers we just ask for singles and earth.
Then you asked for the wrong type of cable!! Singles WITH cpc would have made them think as well as your outfit
 
it’s single red with sheath, single black with sheath. Then a 1mm cpc solid green around all the accessories. The spec here for councils is still to wire in singles and cpc sheathed Both live and neutral must contain the cpc. In wholesalers we just ask for singles and earth.

There is no regulation I know of that requires a cpc in sheathed cables, so no code there. Unless your eicr is being carried out to a different spec.
Cpc is undersized if unsheathed though by the sounds of it.
 
There is no regulation I know of that requires a cpc in sheathed cables, so no code there. Unless your eicr is being carried out to a different spec.
Cpc is undersized if unsheathed though by the sounds of it.
Some thing to do with unprotected cpcs should be protected, conduit or trunking or mim 4mm I believe, and for the OP you can get single cable sheathed and including a cpc.
 
Yes we have to wire with the singles combined with cpc that’s all we use for lighting circuits that’s the spec. My question is to the separate cpc not having mechanical protection. I was always taught this should be 4mm and if protected 2.5mm. I have made a note in summary of the condition of the installation. Just unsure of what section if any to code it in inspection schedule.
 
Yes we have to wire with the singles combined with cpc that’s all we use for lighting circuits that’s the spec. My question is to the separate cpc not having mechanical protection. I was always taught this should be 4mm and if protected 2.5mm. I have made a note in summary of the condition of the installation. Just unsure of what section if any to code it in inspection schedule.
Why is it the spec to wire in singles seem very outdated? but not against the BS, are these circuits wired in Steele conduit and trunking, and the installers don't know how to utilise the containment as the cpc?
 
Sounds like whoever did the installation didn't have any single and earth and so, as a result, wired in separate singles. Bad news.
Edit. Never seen any double insulated g/y single. Maybe a case for it?;)
 
Last edited:
Why is it the spec to wire in singles seem very outdated? but not against the BS, are these circuits wired in Steele conduit and trunking, and the installers don't know how to utilise the containment as the cpc?
Just the local councils spec. No steel conduit or containment just the singles and earth. Clipped direct to joists and oval tube plastic drops to accessories on walls. We just get the specs that there electrical design team issue.
 

Reply to 1mm single around lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all EICR today on a ground floor flat .. 1 issue .. At the consumer unit there was a 1mm core with its yellow (sleeved brown) in a 20A radial...
Replies
20
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
488
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
783

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock