New build 2 storey extension, block internal walls to be plastered over whats best?
1) chase in conduit or
2) surface, metal or pvc channel.
whats the best size metal back boxes to use ie lighting switches using dimmers ( I know the backs of these can vary alot) but customer hasant decided wich ones yet, dont want to put to smaller box on wall and have to change it after plastering? Is there a one size fits all? And how far would you leave back boxes protruding from block work for plastering? cables not in safty zone but will be RCD protected.

thanks for any advice guys.
 
Last edited by a moderator:
Put a 35mm in that should cover nearly all dimmers, if you need a 45mm then that is some dimmer.

If block you mean breeze or thermolite etc then if you want it flush you will need to chase it in. IMO chase and then oval tube to protect the cable from plasrerers, but oval tube is not necessary.

Normally only leave back boxes proud if the wall was being dry lined, are they? If it's plaster then cut them flush with the block, unless you think the plasterer is going to welly on loads of coats, for some reason.

Why are you not running in zones? You should
 
Sorry about the zone bit they are run vertically,horizontally from switches and sockets, I meant to say there not 150mm from top of wall and 150mm from corners, oops. one to many Shandy's last night. the walls are thermo lite and will be plastered, a bit like me last night.

sorry for confusion guys
 
Thermolite mate just chase in some oval, you can chase that stuff out with a dessert spoon! Again as it's thermolite and easy-peasy, you may as well use the deepest boxes you can get your hands on.
 
Most houses in northern ireland are all done in block walls just plastered and we always use 20mm conduit. it is easier to get cables down than oval conduit. I definitely was use a conduit of some sort I would not be happy with the cables just being plastered into the wall. For the switches I would use 35mm boxes and sockets i would use the 25mm boxes. Leave them nearly flush with the blockwork.
 
Hawk81 the conduit is chased and flush with blocks?
and is that metal or PVC?
why not use metal or PVC channel and save chassing into the wall?
that was the point of this post.
 
Last edited by a moderator:
Unless otherwise asked for, I would run cables down on the block and use capping to cover, whether drylined or wet plastered.
25mm back boxes surface mount if drylinig, sink in about 15mm if wet plastering.
 

Reply to 1st fix Chassing and back boxes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
843
An odd question granted but bear with me. I've got to extend a radial circuit in a community centre to fit a new hand dryer in the toilets, but I...
Replies
15
Views
3K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
Hi All. What is the best/preferred method when connecting 20mm conduit to a back box of a socket on an outside wall ? I am connecting a BG...
Replies
10
Views
3K
I have a customer who lives in a grand old house which suffers from damp. The ground floor sockets (2 different circuits) IR test at around...
Replies
21
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock