I have been installing a 3 phase 60KvA generator connected to a MDU with a 100A 0.1A RCD, when I test the earth electrode resistance (Ra) using the earth fault loop impedance tester I get a reading of 1845 ohms, as this does not meet the Ra x Ia less than or equal to 50v, 1845 * 0.1 = 184.5 , it fails this test.

The ground seems quite dry and the earth electrode rod is under trees, I have tried moving the earth electrode, but still cannot get the Ra value less than 1845 - Have you got any suggestions as to how I can reduce the Ra ?
 
1. You are not competent to be installing a large genset such as this without some knowledge of earthing.

2. Please see my earlier post, you cannot use an earth loop impedance tester on this set up, draw a diagram if that'll help you..
 
one metre, I have also tried moisting the area with water, this does bring the reading down a little but not substantially

One meter...??? A one meter rod is nowhere near long enough. Even if by some miracle you got a decent Ra value it won't be stable at only 1 meter depth.

Organize at least 2 x 2.3 meter rods and a threaded brass coupling. Knock in the first rod, attach the coupling and screw the second rod on top of it. Knock the second rod in so your depth is around 4.5 meters. Now take a new Ra reading with an earth rod tester.
 
Do as suggested by Marvo, and move the earth rod position away from any tree's, the roots will rob the surrounding ground area of moisture around the rod. Do not use the thin 3/8'' twigs if that's what you have installed they are the next best thing to being completely useless, apart from not being able to extend them. Use extendable 5/8'' 1.2m rods, which you'll probably need at least 3 if you take Marvo's good advice, or better still 2 X 2.4m rods. Depth is the real key to obtaining both a good Ra value and to ensure the overall stability of a TT system....
 

Reply to 1st Generator install in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
397
Hi. I have a UK customer that has an agricultural building that will have a Diesel TPN generator supplying a corn dryer electrical installation...
Replies
1
Views
1K
Hello everyone my name is Tarek, i work as a concert and show lighting operator with over 20 years of experience in this field, so i have gained...
Replies
1
Views
2K
Evening everyone, Looking for a bit of advice with generator earthing/testing. An 80kva generator supplying a small site with a few portacabins...
Replies
1
Views
4K
Here is my dilemma. Picture this arrangement: a system with a 100A three-phase supply will have a RCD incomer (and possible some generator...
Replies
9
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock