Hello I hope you are well, I have a 6mm socket radial with two sockets on the circuit, the circuit Protected by a 32A MCB is it okay to spur clipped direct to one double socket, thanks Andi
 
Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members

telectrix

-
Mentor
Arms
Esteemed
it is OK IMO, as 1 double socket cannot overload the 2.5mm unless you are plugging in 2 x 3kW heaters, in which case the socket will probably fail first.
 
Why not just carry on with 6mm...?
 

telectrix

-
Mentor
Arms
Esteemed
Why not just carry on with 6mm...?
unless he's coming from the last socke on the radial, he'll not be able to get 3 x 6mm in a terminal.
 