Can i scratch your head (bare in mind biggest i have done is 25mm 4core ?)

I am tendering for a big house new build

I think they already have 100tpn
(But in a kiosk 40m away from house)

And i think they are doubting its big enough now (they sent max demand table below)

So they are asking for a price for 200a tpn sub mains to house if they upgrade from 100a to 200a tpn.

Am i right that the swa from kiosk to house (40m through underground duct)

Will need to be 150mm 4c with a 120mm cpc

And its just bad design that the income is so far from the house and needs a swa sub main!
 

Attachments

  • 22595E99-DF8F-47AF-923D-C8A8D392BDC2.jpeg
    161.2 KB · Views: 64
Last edited:
I haven't calculated it but 240.0 sounds well oversized. For ease of installation parallel cables are often better and I would have thought a pair of 70.0s would suffice but it needs calculating using a 2% vd. The cpc size will need calculating and it must be of a csa to support the main protective bonding but again 185.0 seems oversized.
 
Is that table showing single phase loads or 3-phase?

If it is the sum of single phase then it is below 300A so with tolerable balance a 100A 3-phase feed sounds enough to me. Or have I missed something here?

In any case 200A 3-phase and 3% drop on-line calculator is coming out at 120mm, added CPC of 70mm to 4 core SWA might be OK but obviously need to look at Ze and end of cable Zs for 5s disconnection.
 
OK looking at some of the examples it looks like they are 3-phase loads so it is really adding up to that sort of value.

But if they use only 1/4 of the diversity-allowed current it is going to cost £125/day!
 
some of the circuits will be three phase- like car charger, GSHP, ASHP etc

should you only divdide 189/3 if all circuits are single phase?

Am i right that the swa from kiosk to house (40m through underground duct) so ref method D for three phase cable:

Will need to be 150mm 4c with a 120mm cpc for a 200a sub
Or if they stick with 100a sub- a 50mm 4c with a 35mm cpc will be adequate?
 
some of the circuits will be three phase- like car charger, GSHP, ASHP etc

should you only divdide 189/3 if all circuits are single phase?
However you do it, do it consistently. Looking at some of the numbers (e.g. downlights) you seem to be doing it the 3-phase way (i.e. total power / (230 * 3) = 3-phase current) but check you really are consistent.

Also at some point plan the loads so they are fairly well balanced per-phase. The bigger ones are by design, but otherwise look at how they get allocated in the TPN board(s), or how you split out SP sub-boards, etc.
Am i right that the swa from kiosk to house (40m through underground duct) so ref method D for three phase cable:

Will need to be 150mm 4c with a 120mm cpc for a 200a sub
Or if they stick with 100a sub- a 50mm 4c with a 35mm cpc will be adequate?
Depends on supply Ze as well as volt drop. 35mm should be OK for 100A only on CCC but at 40m it is almost certainly going to be VD or R1+R2 that is your issue.
 
Looking at page 367 of the BBB, a BS88 fuse rated at 200A has 5s disconnection at 1200A. So your Zs for cold-checked cables and Umin is given by:

Zs = 230 * 0.8 * 0.95 / 1200 = 0.146 ohm.

You need to know Ze to allow for R1+R2 but assuming my example of 120mm & 70mm CPC it is:

R1 = 0.153 mOhm/m
R2 = 0.268

For 40m = 40 * (0.153 + 0.268) = 0.017 ohm, hence Ze < Zs - (R1 + R2) = 0.146 - 0.017 = 0.129 ohm

Pedants might query the use of DC values of R1+R2 instead of AC impedance, I leave that as an exercise for the reader...
 
A quick check shows you can meet 3% voltage drop with 50mm at 200A so the above cable calculator values really are coming down to CCC.

So 120mm is going to meet even 2% VD as well as the CCC. Running a parallel 70mm CPC would meet Table 54.7 of course, but realistically 35mm is going to be fine on adiabatic for 200A fuse.

Looking at using a pair of cables and assuming grouping of 0.8 then you need 125A CCC per cable. For 70C limit you need 70mm 4-core (Table 4D4A column 7), for 90C it is 50mm (Table 4E4A column 7).

Running 90C is worrying to me as not all accessories will be happy or long lived at that, so I would go with 2 * 70mm just as @westward10 suggested. For the CPC another 70mm would then meet Table 54.7 as well, though if you check adiabatic and resulting Zs you might just find 35mm is perfectly good.

EDIT: In reality this is a house, not an industrial plant, so it is very unlikely they will hit 200A for any length of time, so specifying 50mm 90C design cables is not unreasonable if you check that the planned supply switch-fuse and main DB isolator are rated for 90C use and can cope with 2*50mm, etc.
 
Last edited:
Just to clarify the above, 2*50mm in duct looks to meet the CCC,

If you specify free air / perforated cable tray on the Doncaster cable calculator it comes up with this as suitable:

Single Core 90°C Thermosetting Insulated Cables, Unarmoured, With or Without Sheath

Tables Apply to: 6491B, 6181XY

Voltage: 400V

Load: 110.85kW / 200A

Length: 40m

Method of Installation: In free air or on a perforated cable tray

Cable Size: 50mm²


It was just a quick check on volt drop to see what would be possible without having the tables to hand.
 
If you have only ever put in 25.0 then 120.0 is going to be a whole new experience over 40m. Personally I would use parallel 70.0s and that is still a task there are however companies you can sub this out to who have all the equipment and specialise in just this kind of thing.
 
Another option is tripled cables? Looking at OSG table F3 grouping would be 0.7, so per-cable CCC needed is just under 96A for 200A total. That is met for 70C at 35mm (or at 90C for 25mm).

You would need fairly big duct to get 3 * 4C 35mm + a 35-70mm CPC run through, but if you end up doing it without a lot of experienced/tooled-up help it might save you a lot of pain even though cost is not hugely different to a 4C 120mm solution.

The problem with cable CCC is the loss is I2R so for a given ability to get rid of heat you need 4 times the CSA for double the current. It is not always quite so bad as bigger cables can get rid of heat faster, but that depends to a degree on the surface area which goes up roughly with sqrt(CSA) and might well be further restricted by the overall size of duct, etc, so you still see a painful increase in cable size, cost and wrangling difficulties.

Edit: Just to add 35mm should meet adiabatic for 200A fuse so fancy protection for members of the paralleled set should not be required.
 
Last edited:
I guess taking this to its logical conclusion, how about 4 * 95mm AWA single core copper cables and a 50mm CPC in suitably sized twin-wall duct (e.g. 160mm OD / 140mm ID)?

You would need non-ferrous gland plates and to carefully identify each conductor, etc, as well as checking the gland type for use with aluminium armour, but each conductor is going to be far easier to wrangle and you don't have any issues of how to terminate 2 or 3 parallel conductors at the end points.
 
I haven't calculated it but 240.0 sounds well oversized. For ease of installation parallel cables are often better and I would have thought a pair of 70.0s would suffice but it needs calculating using a 2% vd. The cpc size will need calculating and it must be of a csa to support the main protective bonding but again 185.0 seems oversized.
240 oversized, bigger than the street cable! more info needed!
 
240mm took me 2 days to terminate the ends, as mentioned above, a whole different game to playing with 50 and under .
 

Reply to 200a tpn for house?! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a customer who has a kiosk with 100 amp cut out fuse supplied from UK power, he needs to bring the power 178 meters to his house, He...
Replies
8
Views
893
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
561
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock