Hi folks, I have put a new light circuit in a domestic property and am finding 200v on the earth conductor which is tripping rcd as soon as l switch the breaker on. With the circuit in question dead with all 3 cores out of the cu I test between L+E and N+E but am getting no continuity as soon as I power up the circuit though the voltage is there again. Any ideas where the voltage is coming from or how best to test for it would be greatly appreciated.

Thanks in advance guys an gals
 
Earth been used as a switch wire or strapper?

Although you say you installed the lighting circuit...

The only other time I had something like this was on a large fan with flexi duct either side, the case was sitting at 150v!
 
Had a fault find callout for the exact same thing, as odd as it sounds check your connections, we found a connector with feeds in was loose, the earth was carrying 230 to neutral and no voltage on lives, once we tightened the connector block we got voltage between live and neutral! Odd I know, but worth a go!!
 
Hi folks, I have put a new light circuit in a domestic property and am finding 200v on the earth conductor which is tripping rcd as soon as l switch the breaker on. With the circuit in question dead with all 3 cores out of the cu I test between L+E and N+E but am getting no continuity as soon as I power up the circuit though the voltage is there again. Any ideas where the voltage is coming from or how best to test for it would be greatly appreciated.

Thanks in advance guys an gals

What did your dead tests show?? R1 + R2??
 
Nail through cable tracking down to earth through building, usually capping nail catching live or neutral, had this before on a call out was fine for however long circuit was in for (I never put it in) then tripping Rcd occasionally and then all the time, when ir testing fault would come and go live earth.
 
If you've downlights with drivers then it's not impossible (though unlikely) that one of them might be faulty or internally mis-wired, but my money would be on a cabling/connection issue somewhere and/or a polarity crossover.
 
Hi folks, I have put a new light circuit in a domestic property and am finding 200v on the earth conductor which is tripping rcd as soon as l switch the breaker on. With the circuit in question dead with all 3 cores out of the cu I test between L+E and N+E but am getting no continuity as soon as I power up the circuit though the voltage is there again. Any ideas where the voltage is coming from or how best to test for it would be greatly appreciated.

Thanks in advance guys an gals

Which two points are you actually measuring this 200V between?

If the voltage is present only when you power up the circuit and then trips the RCD as soon as the breaker is switched on, how is the voltage present long enough for you to measure it?
 
Have you tried to split the circuit down? To see if the fault is in the first half or second half. Simple things like this make it much easier to narrow a fault down
 
Hi folks, I have put a new light circuit in a domestic property and am finding 200v on the earth conductor which is tripping rcd as soon as l switch the breaker on. With the circuit in question dead with all 3 cores out of the cu I test between L+E and N+E but am getting no continuity as soon as I power up the circuit though the voltage is there again. Any ideas where the voltage is coming from or how best to test for it would be greatly appreciated.

Thanks in advance guys an gals

Sorry but I'm struggling with this one.....you've obviously got an IR fault to earth and you are disconnecting the earth from the CU in order to power up in which case a voltage is going to appear on the now un-earthed earth wire.....and your checking continuity?
 
Hi folks, I have put a new light circuit in a domestic property and am finding 200v on the earth conductor which is tripping rcd as soon as l switch the breaker on. With the circuit in question dead with all 3 cores out of the cu I test between L+E and N+E but am getting no continuity as soon as I power up the circuit though the voltage is there again. Any ideas where the voltage is coming from or how best to test for it would be greatly appreciated.

Thanks in advance guys an gals

Just carry out tests per normal on the newly installed circuit as your training, Dead tests first to confirm continuity of all cores and then R1&R2 tests, Polarity will then be confirmed before energising, never energise a circuit before testing, you may get a fault and 200 volts may appear on a Circuit protective conductor :confused5:
 
As said break the circuit back down and check IR's, can only be pressure fault behind a switch, damage to a cable or one of your connections has gone a bit off piste ?
 
Whats a dead test? will my roll of tape help me with this?

a dead test is carried out by paramedics after you have energised a faulty circuit that you have not properly tested. they try to find a pulse. if there is no pulse, then you are dead.
 

Reply to 200v on the earth conductor of my lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
575
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
545
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
411
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
600
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
242

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock