A final ring circuit. A 20A switch spur off the ring feeding a single 13A socket supplying a Modem in a large plastic Modem box. The spur is restricted to 13A and only one outlet, appearing to conform. Do regs say the fuse has to be at the tapping of the ring?
 
Reaction score
68
Think grid switches for kitchen appliances.
20A DP switch as spur point off the rfc.... each spur is unfused to one point. Be that a socket or whatever.

the spur only needs a fuse if it is then supplying more than one point.
Yes, a fuse will be on the spur, being a 13A socket it has to be. Yes, gridswitching makes it clear the fuse can be downstream from the tapping on the ring, as long as the spur cable is protected. thx
 

ipf

-
Mentor
Esteemed
Arms
Reaction score
5,073
You can spur once from RFC's at any point. Any outlet point, any cable (joint box) or at the circuit origin. Imagine FCU's at the side of sockets, under floorboards or inside consumer units, even, for every single spur point.
 
Reaction score
68
Appears people get confused at taking a spur from behind a socket. The terminals of a socket act as a junction box for the main current carrying spine of the ring. Theoretically, a socket is a spur off the main ring - look at the brass bits inside it to the three pin receivers, they spur off the terminals.
 
Reaction score
68
The opening question was solved. As long as the spur is protected by a 13A fuse, at any point along it, then all is well. You can have as many switches on the spur as you like then.

Bus bars?
 
Last edited:

ipf

-
Mentor
Esteemed
Arms
Reaction score
5,073
That conflicts with others here. Ref?
If you put individual FCU's for each point on an un fused spur, the additional points could lead to the load being too high for the spurred cable. With an existing spur, for example, all additional loads should be via one FCU.
 
Last edited:

loz2754

-
Esteemed
Arms
Reaction score
1,713
If you put individual FCU's for each point on an un fused spur, the additional points could lead to the load being too high for the spurred cable. With an existing spur, for example, all additional loads should be via one FCU.
I believe John said switches, not FCUs


Hang on a minute! I can't believe I'm defending the Wago busbar advocate! 😜
 