Aaron b

Mentor
Esteemed
Arms
Reaction score
334
Hello, I changed a socket over earlier and tested the circuit after. The fault current was 20kA, Am I right in thinking I only need to consider the breaking capacity of the service fuse that's likely to be 80kA? I'm struggling to find any reference material.
 
20KA, more details needed, can we have details of the supply, photos of the supply meter, cutout and consumer unit. Please measure distances.
It's a tns supply fed from a pole mounted transformer about 15m away. Lead sheathed cable with a pipe clamp providing the earth. 2.5mm cable feeding the socket about 1.5m from the intake. It's a 60amp supply. Just upgraded to a smart meter. The guy done a nice job and sorted out the mess the PV guys made years back. It's a white plastic wylex board with a wooden back.
 
That is an unusually high fault current and MFT results at these levels can be rather inaccurate. The problem is that when the impedance is low, many ordinary instruments can only measure it with low resolution, so when the fault current is calculated from the impedance it can have large hidden errors.

Was the 20kA calculated by the MFT and if so what was the associated impedance measurement? An Ipf of 20kA implies an impedance of 0.0115Ω but even an error of say 0.01Ω due to incorrectly compensated lead resistance would bring the current down to 10.7kA. That might not get your rewireable fuse off the hook, but it's worth being aware of this source of error in Ipf readings.
 
It is higher than the prospective fault current advertised by some DNOs. I would suggest asking the DNO what is the the actual fault current. It may also look like a board change required with regards to the 3036 fuse links.
 
I think you are probably right. I just ran a couple of Z's tests on a socket in my property and was getting massive L-N currents. I was zeroing using the plug clip thing but trying a different one brought down the readings to something more reasonable.
 
That seems astonishingly high for that sort of a setup. The 500kVA transformer that feeds our supply point is only 11kA (three-phase bolted fault, I measured 5kA L-N which would be 10kA 3P fault at that point)!
 
It is higher than the prospective fault current advertised by some DNOs. I would suggest asking the DNO what is the the actual fault current. It may also look like a board change required with regards to the 3036 fuse links.
The site definitely needs a upgrade and hopefully it was the zeroing thing throwing me out.
 
It looks like the TIS clip is reading 0.2ohms higher than a fluke one on the live lead. Unfortunately the meter only flashes up with the calibration values for a second so I'm going to have to keep an eye out for that.

Thanks everyone for your input.
 
Last edited:
I think you are probably right. I just ran a couple of Z's tests on a socket in my property and was getting massive L-N currents. I was zeroing using the plug clip thing but trying a different one brought down the readings to something more reasonable.
Hi,
As you are a trainee I would suggest you ask your local DNO what is their normal advertised PSCC and also disucss https://www.beama.org.uk/asset/1E3E6D54-6091-47E0-805FBA161841A309/ with your supervisor. Eitherway I suspect that 3036 board needs to come out.
 
Hi,
As you are a trainee I would suggest you ask your local DNO what is their normal advertised PSCC and also discuss https://www.beama.org.uk/asset/1E3E6D54-6091-47E0-805FBA161841A309/ with your supervisor.
That is a useful guidance note to keep on hand.
Either way I suspect that 3036 board needs to come out.
Very true.

While they are still considered "OK" for some existing installations, they have a number of significant drawbacks in terms of no RCD/RCBO options internally, limited breaking capacity (as discussed here), sometimes wooden backs so poor fire rating, and, most importantly, few of the general public are competent to change fuse wire.

Also it was usually the lights that would go, and then you had the added joy of trying to rewire in the dark :(

Not to mention the unpleasant result if someone fails to heed the instructions about switching off and plugs a rewired fuse back on to a live fault.
 
Last edited:
I've been working on industrial sites for over 10 years but I'm going through the NVQ to formalize my qualifications and to be able to get part p registration but clearly I'm a bit green with some of the domestic stuff. Thanks for the idea on calling the dno, it's not really an area I've had to deal with in industrial scenarios.
 
Presumably you had the ATT function off in doing the Ze test was it?. Anyway, if you read the manual on your MFT you will find that the figure you are looking at could be 6 digits up or down from what you are reading. So you could have 0.07 which could be seen as 0.1 which then means your PFC is 2.3ka (to 3.3Ka) Usually a type II main fuse (old) 1361 is rated at 33Ka Type I 16Ka so depends on type, and yes it may be counted as safe by regs. Of course your original figure would far surpass the Icn of the MCB no doubt. Actually I suppose that is another way of saying what @pc1966 said.....
 
Presumably you had the ATT function off in doing the Ze test was it?. Anyway, if you read the manual on your MFT you will find that the figure you are looking at could be 6 digits up or down from what you are reading. So you could have 0.07 which could be seen as 0.1 which then means your PFC is 2.3k. Usually a type II main fuse (old) 1361 is rated at 33Ka Type I 16Ka so depends on type, and yes it may be counted as safe by regs. Of course your original figure would far surpass the Icn of the MCB no doubt.
What MCB was being discussed?
 
What MCB was being discussed?
I am taking a big leap here and assuming there will be a circuit in a consumer unit that houses an MCB which will no doubt be subject to the fault. I assume if there was not an MCB then the PFC would not really mattter as there is no circuit to cause a fault. Could be wrong though...I do see what you are referring to though as the 3036 being mentioned but even that could not withstand a fault of that level.
 
I am taking a big leap here and assuming there will be a circuit in a consumer unit that houses an MCB which will no doubt be subject to the fault. I assume if there was not an MCB then the PFC would not really mattter as there is no circuit to cause a fault. Could be wrong though...
Hi,
Look up 3036 fuse in the regs.
 
Why dont you just tell me what you are getting at, can't be bothered to do so right now, bit tired and having a relax? Could you be referring to 2Ka, whats on your mind?
 
Last edited:

Reply to 20kA ipf on 15A 3036 fuse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
670
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
771
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock