D
domino
Help!
Currently doing the practical test for Level 2 2330. Have to inspect and test this week coming. I think I have a good grasp of all the dead testing we need to do BUT have just been swotting up in the Onsite Guide and I've found something that has not been mentioned so far at college.
One of the circuits is a length of 2.5mm² 3 core SWA from a consumer unit to a surface mounted metal clad Fused Connection Unit. The CPC is one of the 3 conductors but of course the armouring is also earthed at both ends.
We need to enter an R1+R2 value on the test sheet for this circuit but according to the OSG, Method 1 can't be used for swa or micc cables. We definitely haven't been taught this yet, so I was wondering how you guys obtain this value in the real world?
I do appreciate there are 2 parallel earth paths down the cable. Would you remove the armouring earth connections and measure across phase and earth? Or maybe connect both earths and phase and record that reading?
Help!!
Currently doing the practical test for Level 2 2330. Have to inspect and test this week coming. I think I have a good grasp of all the dead testing we need to do BUT have just been swotting up in the Onsite Guide and I've found something that has not been mentioned so far at college.
One of the circuits is a length of 2.5mm² 3 core SWA from a consumer unit to a surface mounted metal clad Fused Connection Unit. The CPC is one of the 3 conductors but of course the armouring is also earthed at both ends.
We need to enter an R1+R2 value on the test sheet for this circuit but according to the OSG, Method 1 can't be used for swa or micc cables. We definitely haven't been taught this yet, so I was wondering how you guys obtain this value in the real world?
I do appreciate there are 2 parallel earth paths down the cable. Would you remove the armouring earth connections and measure across phase and earth? Or maybe connect both earths and phase and record that reading?
Help!!