Hi Steve
Just did my three little exams last Friday, Sorry at work at the mo but will pop up a propper answer later tonight, feel free to pm if you like.
Cheers
Duncan
Hi Steve
Sorry it's a bit late but just got in Fuggin work!!!
I'm just like you been working a none sparky job and learning at college, although the last six months been doing my owne domestic jobs and the odd bit of commercial. Quite interesting and nothing like the stuff you do in college some jobs good (£) some utter ****e!! live and learn.
Right down to bussines
just had my written and three little exams (big fella on Wed's
The inspection board at college (Poole Dorset) comprised of a very simple set of circuits.
In the Middle a CU with 4 ways and fed from a double pole switch (not live) with the incoming tails & Main Earth cut of below the board. No covers on (this was not a fault )
First fault was on the Bonding, it had no warning lable on the earth tag on the water pipe. so quite easy
First Circuit: lighting circiut fed from 6A bs1362 in 1mm out of top of CU into a ceiling rose, then onto a 2 way switch (all covers off not a fault)
Second Fault: open gromit in CU for the 1mm, so not IP4X should be a closed one
Third Fault: Insulation cut back to far entering ceiling rose, exposing conductors.
Four Fault: To much copper conducter showing on phase entering termination of three plate rose.
Fifth Fault: No sleaving on wires in two way switch, E.g no idea of switch wire or common live
Second Circuit: Switched Fused radial fed from CU of 20A Bs1362 in 2.5mm Tw&e
Six Fault: load side of SF wired incorrectly. L in N.
Third Circiut: Radial in 2.5mm to 2 13amp sockets from 16A 1362.
Seventh Fault: No sleaving on CPC
Eighth Fault: Cable clipped up twisted on its side.
Nineth Fault: Bend radiouse to tight on cables.
Tenth Fault: shedule says 16A but has 32A in place. over rated.
Fourth Circuit: 6mm SWA to garage door via 20A 1362
Elleventh Fault: No fly lead to banjo nut for cpc, so steel wire not earthed
Twelevth Fault: Neutrals and lives all numbered but not in matching holes on neutral bar.
Hope that lot helps mate???
and good luck
Cheers
Duncan