Discuss 2391 Practical re sit, Need a little bit of help... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
74
Hi all,
On friday I have the re sit for my 2391 practical, I'm confident on all the dead tests, Zs, RCD's and functional checks etc. And I'm fairly confident with the PEFC and PSCC, However on our test rig we have 2 boards (A main board, and a 'Garage' board) So do I need to do the PEFC and PSCC at both boards?
Thanks in advance.
 
I've just done my 2392. My understanding (and I'm sure I will be corrected if I have this wrong!), is that BS7671 requires the PFC (PEFC+PSCC) to be determined at the origin and at other relevant points. For simple installations, where all circuits eminate from the CU, that would be there. In the 'your' installation, the PFC should also be determined at the garage CU. My notes read that PFC should always be determined at the point of the installation where the electrical energy is deliverd. Only the same as for determining the ZS of those circuits.
 
Your main board should be supplying your garage board.

The main board is where the supply comes in to the installation. So you need to take Ze and PSSC/PEFC at that point.
You then have a submain from your main board supplying your garage board, this is a distribution circuit.
You have a choice, either measure Ze PSSC/PEFC at the garage board, and record the result as Zdb, or calculate them, whichever floats your boat.

Cheers..........Howard
 
Thanks all, I think finding the PEFC at the garage board should be alright, just do it as I would measuring the Zs but just press the PFC button. I assume the PSSC will be the same as for the main board. I just need to make sure I have the 'garage' breaker ON at the main board.....I think....
 
Thanks all, I think finding the PEFC at the garage board should be alright, just do it as I would measuring the Zs but just press the PFC button. I assume the PSSC will be the same as for the main board. I just need to make sure I have the 'garage' breaker ON at the main board.....I think....

Yep it's one of the live tests, before energising the garage circuits, test for PFC & PSC (record the worst figure, ie. the highest ka). The garage cu isolator will be in the off position, you are testing the distribution circuit from the garage CU back the house CU back to the supply transformer. Record as Zdb as Sirkit said (additional record of schedules & test reports to your EIC/EICR). You should carry out your garage CU ZS test before PFC tests.
 
Last edited:
Have a think about WHY you would do a PFC at the sub board and what you would use that result for (whether measured or calculated). It is not good enough to just record a result because the form has a box that needs to be filled in. There is a reason for this particular test.
 
The PSCC and PEFC should be at the highest at your main CU. With ohms law taking effect, the run to the garage will add more resistance to the circuit and so your PSCC/PEFC at the DB in the garage should be lower.
 
Like the other chaps just said, what is the relevance of the PFC an PSC, when would you get those currents? What would currents of that magnitude do? Would a low or high result be desirable? Answer those questions and you'll understand why you're doing it.
 
As far as I understand the reason we need to do the test is, to make sure that equipment (breakers) can cope with any potential fault currents. But thank you all for your help. I passed it today, and was very relieved to do so. AM2 in a few months time, so hopefully before long all the 4 years hard work will have an end product.
 
Having spent my 4 year apprentiship in the modular building industry the motor's arent the most concerning thing, It's the bloody S plan heating system. I'm hoping they'll take pitty on me and let me put a 2kw Convector heater on a concealed stat....
 
If your up to speed on motors and dol starters etc,s plan and heating wiring is a peace of cake,y plan is slightly more hard to fathom when new to heating control wiring and fault finding,but you soon get to grips with it,for an s plan there are wiring diagrams on the forum so you could print one off and practise,its not as complex as you think,all controls have L-N-E then just MVs have grey(perm L)browns are switched either by a roomstat or cylinder stat,when calling for heat,MVs motor and the orange is energised(connected to switched live of boiler) simples! well done on passing the 2391
 

Reply to 2391 Practical re sit, Need a little bit of help... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
701
Hi all, first post so go easy! This is for people who are looking for more info on the course and exams and is from my experience of doing the...
Replies
1
Views
3K
Hi all, ive found myself in a bit of a desperate situation here. I sat my compex 10 months ago and failed sections 01 and 04. I was meant to...
Replies
1
Views
9K
So i've been doing electrics for several years now, and am going for my 18th edition this week. I'm 99% confident i'm going to pass it. After...
Replies
25
Views
5K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock