Hi Guys n Girls
Sorry if im having a dumb momment but I have a practical 2391 exam in march and i cannot remember for certain how to verify Vd.

Im assuming i can calculate the circuit length by taking the r1+r2 reading - then get the m'ohms per/m for both cables from the (OSG P166). Then divide the measured reading of say 0.3 by the milli ohms per metre to get the circuit length.

So do i then just do a simple Volt drop as per P124OSG using cable charts P274 in BS7671, my main concern is how about a 3phase Vd? You may not b surprised to hear i missed the Cable calc bit out the written exam... I passed it though lol :D

Just tell me what im missing, im not proud, after all I knew it all once and since forgot it all lol

Thanks
Mark the Spark
 
Last edited by a moderator:
you gont have tyo verify volt drop in the practical however i do recoment you study the periodic test sheets.

Hmmm. :) Ive been flicking throught the books and eventually things starting to come back online with the old brain!. I tried a few calcs and it all looks to be adding up at last..
As for the forms, thats this weekends browsing material LOL :D
I hear their wil be a motor circuit on the board, Im assuming u measure the IR between cpc and PN linked as the motor control will have a coil in it???

Thanks
Mark
 
You can always measure it :)

I didn't have to actually verify the volt drop in mine - the assessor

just asked me to describe how I'd do it.

I just said by measurement or by calculation (the way you described)

except you'ld need the circuit length to do the OSG calculations - could

be a bit tricky on a 2391 board because the circuits contain resistors.

Failing that, find the resistance of the cable, like you said (line and neutral)

and use ohms law with the design current.

Eg.

Lighting circuit:

R1 - 0.6 ohms

Rn - 0.5 ohms

Total - 1.1 ohms

Volt drop = 6 A x 1.1 ohms = 6.6 V

I think :D

R2
 
volt drop is calculated using the desighn current not the rating of the overcurrent device. to truly calaculate it you have to have the true lenght of run, desighn current asw well as cable resistance which is why its frequently limited in a periodic
 
But that assumes a 6 amp load :)

Well I used 6A as an example of the design current - I did say:

. Failing that, find the resistance of the cable, like you said (line and neutral)

and use ohms law with the design current.:)


Like I said though, easiest way is to measure it.
 
you could measure it by taking incoming voltage at source then measuring voltage at end of line. it has to be under load though.


Thanks, Scotsparky, for reminding me of that fact:)

I was thinking you could just measure at the origin and then measure at

the end of the circuit - forgetting that the load counted.

In the 2391 this probably wouldn't be the simplest method then, as most

of the circuits don't have loads attached.
 

Reply to 2391 verfying volt drop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I'm currently doing my assignment for 2357 and was just making sure I'm calculating the cable length for the lighting circuits right. As...
Replies
1
Views
2K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
7K
Morning team Question about volt drop. I presume I am missing something here. So firstly the facts out the OSG. Table 7.1, page 66, lighting...
Replies
20
Views
3K
Select (Scottish) Certification Scheme Question on volt drop from 2391
Hi all, I have worked out the volt drop on other questions using the formula mVxAxM. had no issues, but this question below has just fried whats...
Replies
26
Views
6K
Hi all, I am currently doing my 2391-52 and have been given a mock paper, one of the questions is around vold drop as per below, can someone...
Replies
20
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock