The prospective short-circuit current between line and neutral is measured at 900A. The maximum balanced prospective short-circuit current level between lines, as a rule of thumb, can be assumed to be approximately:

A: 0.9 kA
B: 9 kA
C: 90 kA
D: 1.8 kA

:banghead:
 
its 1.8kA

In reality, between 2 phases it will be the PSCC between L&N x 1.732

The reason we are taught to multiply by 2 is to account for a possible short between all three phases at once.
 
A= Amps
kA= Kiloamps

So convert amps to kiloamps and if you have GN3 there's a hint about three phase PSSC in there.
 

Reply to 2392 Question - Balanced prospective short circuit current between lines in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock