Hi all,

Hoping for some guidance, which would be much appreciated.

I currently have some Florescent Lights under my kitchen cabinets operated by a light switch and would like to replace with LED strip lighting.

I have purchased some 1 Metre 240V LED strip which is fitted with a 3A UK plug.
50645
Is it a simple as removing the plug from the LED strip and wiring the Live and Neutral into the Junction box of the existing lights?

Thank you in advance, much appreciated!
Aidan:)
 
SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members

telectrix

-
Mentor
Arms
Esteemed
yes.
 

Pete999

-
Arms
Esteemed
Yes, providing the JB is accessible or MF if it isn't
 

DPG

-
Arms
Esteemed
Advent Win
What the old guys said above.

Obviously ensure the circuit is dead.
 

Pete999

-
Arms
Esteemed
What the old guys said above.

Obviously ensure the circuit is dead.
Tel, we are going to have to complain to the Mods, all this ageism is freaking me out:p:mask::eek::mask::mask::kissingheart:
 

DPG

-
Arms
Esteemed
Advent Win
Make sure the cable from the junction box is secured also, either by cord grip or p clip etc.
 

Strima

-
Arms
Esteemed
It would also be advisable to ensure the protective device is the same rating as supplied by the manufacturer.
 

DPG

-
Arms
Esteemed
Advent Win
Good point. Is this junction box fed from an FCU?
 

Spoon

-
Mentor
Arms
Esteemed
I was thinking about this as well.
I presume that the fuse in the plug will be 5A and the existing florescent lights would be connected to a 6A breaker. The cable and switch on the LED should be capable of taking 6A instead of 5A.
Yes, lots of presumptions there...
 
  • Thread Starter Thread Starter
  • #10
Hi all, thank you all so much for your responses.:praying:

The Junction box for the existing florescent lights are not attached to an FCU, only a 6A breaker at the consumer unit.

As the LED lights are factory fitted with a 3A fused plug, would this cause a problem if the plug was removed and connected directly to junction box?

Many thanks once again, i can only apologise for the ageism comments! :p

kindest regards gentlemen!
Aidan
 

DPG

-
Arms
Esteemed
Advent Win
Out of interest what do the manufacturer's instructions say?

Note to George - I know they don't have to be rigidly adhered to.
 
  • Thread Starter Thread Starter
  • #12
Hi DPG,
Unfortunately, they did not come with any instructions whatsoever. Purchased from amazon, most likely a cheap Chinese product...
 

Strima

-
Arms
Esteemed
TBH a 6 amp MCB would operate much quicker than a 3 amp fuse so I wouldn't loose any sleep if it wasn't fused down.
 

DPG

-
Arms
Esteemed
Advent Win
TBH a 6 amp MCB would operate much quicker than a 3 amp fuse so I wouldn't loose any sleep if it wasn't fused down.
There was a discussion about that very subject on here a few months ago. It related to a question about fans.
 
  • Thread Starter Thread Starter
  • #15
Thank you all for your input. Its very much appreciated. I have since connected the LED strip to the Junction box, all seems good - no issues!

Cheers :clapping::praying: