Labeled Exterior Setup and NEC225.30 Question-page-001.jpg

Hey Guys,

Hopefully this picture is clear enough to read the text boxes (if not, the PDF attached should be clearer). I'm trying to get 240V ran to my detached condo garage in order to run my TIG welder and my plasma cutter. I live in Ohio, and I know they still operate under NEC 2017. I want to apply for an electrical permit, but before I pay for the permit submission, I want to be sure this is even POSSIBLE without violating NEC 225.30?? Could exception 225.30 (B)(1), 225.30 (A)(7), or 225.30 (D) apply here to allow me to run this feeder line to my garage? My HOA bylaws will allow me to upgrade my own personal service meter. Really, my HOA bylaws aren't a barrier at all for this type of utility upgrade. I'm just stumped as to how this can even be done without violating the NEC? I mention NEC 225.30 (A) (7) because I would be willing to buy a home EV charging station and install that in my garage. If, then, this feeder wire was ran to my garage for the purpose of installing a 240V EV charging center... wouldn't that allow me to run new feeders to my private garage space?

Thanks for the advice,
Nicholas
 
View attachment 86716

Hey Guys,

Hopefully this picture is clear enough to read the text boxes (if not, the PDF attached should be clearer). I'm trying to get 240V ran to my detached condo garage in order to run my TIG welder and my plasma cutter. I live in Ohio, and I know they still operate under NEC 2017. I want to apply for an electrical permit, but before I pay for the permit submission, I want to be sure this is even POSSIBLE without violating NEC 225.30?? Could exception 225.30 (B)(1), 225.30 (A)(7), or 225.30 (D) apply here to allow me to run this feeder line to my garage? My HOA bylaws will allow me to upgrade my own personal service meter. Really, my HOA bylaws aren't a barrier at all for this type of utility upgrade. I'm just stumped as to how this can even be done without violating the NEC? I mention NEC 225.30 (A) (7) because I would be willing to buy a home EV charging station and install that in my garage. If, then, this feeder wire was ran to my garage for the purpose of installing a 240V EV charging center... wouldn't that allow me to run new feeders to my private garage space?

Thanks for the advice,
Nicholas
As long as you’re going to draw a permit, you can run power to your garage. Install about a 60 amp GFCI breaker and pull #6 romex underground approved. Buy a main lug only 125 amp panel approved for outdoor use. If you run into problems come back and let us know. You already have 1 ground rod at your service so now you need 2 total and they have to be a minimum of 6 feet apart and use # 6 bare wire to tie them together
 
View attachment 86716

Hey Guys,

Hopefully this picture is clear enough to read the text boxes (if not, the PDF attached should be clearer). I'm trying to get 240V ran to my detached condo garage in order to run my TIG welder and my plasma cutter. I live in Ohio, and I know they still operate under NEC 2017. I want to apply for an electrical permit, but before I pay for the permit submission, I want to be sure this is even POSSIBLE without violating NEC 225.30?? Could exception 225.30 (B)(1), 225.30 (A)(7), or 225.30 (D) apply here to allow me to run this feeder line to my garage? My HOA bylaws will allow me to upgrade my own personal service meter. Really, my HOA bylaws aren't a barrier at all for this type of utility upgrade. I'm just stumped as to how this can even be done without violating the NEC? I mention NEC 225.30 (A) (7) because I would be willing to buy a home EV charging station and install that in my garage. If, then, this feeder wire was ran to my garage for the purpose of installing a 240V EV charging center... wouldn't that allow me to run new feeders to my private garage space?

Thanks for the advice,
Nicholas
The articles that you mentioned is for the power company and your main panel. Don’t forget article 110-12 states the you have to install ARCH FLASH stickers on both panel doors
 

Reply to 240V to Detached Condo Garage and NEC 225.30 Violation? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
464
Hello All, Let be begin by making it clear that I AM NOT A PROFESSIONAL ELECTRICIAN! I will be hiring one (I have one scheduled to come out to...
Replies
1
Views
783
Hey, question for the group on grounding when using MC cable and metal boxes.... Situation: Enclosed a carport and turned it into a garage. I'm...
Replies
1
Views
852
I have charged ahead with a small subpanel installation in a detached garage I am converting to a light-duty shop. The setup is simple, but I have...
Replies
1
Views
1K
Hi there. I am not an electrician and ask this question of your forum. My house needs rewiring as the cables although not perished are the type...
Replies
26
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock