i have to send a 75meter run of a 3 core 25mm armoured from the meter to the fuse board. now due to the lenth i have to have a switched fuse and possibly a isolator on the otherside. due to the earth being 25mm i know alot of isolators only take 16mm.

is the use of a helely block perfered to down size the cable one each side?
 
Think you'll find the difference in price between 25 & 16mm swa, is actually cheaper per metre than 6491x, and less hassle installing just one cable. Lees suggestion with the solid copper pin, negates any issues in isolator. Long run mind?

PS, edit not cheaper, looking at the wrong table! But certainly less hassle!
 
Last edited:
Hi Lee and MW, just a dumb question but isn't it ok to use SWA armour as both CPC and main bonding conductor? I haven't done a long run like this and just trying to understand it. May be the Zs is too high without the additional 16 or 25mm conductor, or prohibited by another reg? Cheers, David
 
Hi Lee and MW, just a dumb question but isn't it ok to use SWA armour as both CPC and main bonding conductor? I haven't done a long run like this and just trying to understand it. May be the Zs is too high without the additional 16 or 25mm conductor, or prohibited by another reg? Cheers, David

Hi mate if using another metal for a bonding conductor other than copper which the tables are based on the other metal has to offer at least equivalent conductance. 0.004 is the simplified resistance coefficient per degree C at 20 degree C given by BS 6360 for copper and aluminium conductors. The resistivity of steel (the armour) changes with carbon content. Guidance note 8 gives a value of 8.5.

For example if 10mm copper is the minimum CSA for a bonding conductor for the installation but you was using the armour or the armour was forming part of the bonding conductor then the armour would have to have a minimum CSA of at least 85mm. 10mmx8.5=85mm
 
Last edited:
Got it, thanks !
I looked at my GN8, found table B1 in appendix B. If I'm reading it right the 25mm SWA's armour is man enough if you use 3 core, ha ha, where you won't need it cause you've now got a nice 25mm of cu to use.
 
My guidance note 8 is In the office but from memory you would have to use something like 95mm 2core SWA.
25mm 3core SWA would have an CSA of something around 62mm? which is below 85mm so wouldn't be adequate for bonding but would be fine as a circuit protective conductor. Table 54.7 BS7671 is to calculate/select the cross sectional area of every protective conductor, other than a protective bonding conductor which I think table B1 is based on.....could be table B2 though.
 
The armour of a 2 core 25.0 SWA cable is approximately 6.0 in terms of copper, Lee is quite correct in saying it would have to be at least 95.0 for a 2 core to be adequate to support the minimum size of 10.0 bonding.
 

Reply to 25mm armoured to 16mm earth conductor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
689
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
769
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
265

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock