The requirement to provide RCD protection for cables concealed in walls, was introduced in the 17th.
So nothing was removed in the 16th.
Quite correct error on my part. Nevertheless concentric was but no longer is suitable no matter it's construction.
Probably doesn’t comply, because the standards for con and split con are different to those for SWA.
Have heard in the past, that con and split con are prohibited by ESQCR for use in consumer’s installations.
Not sure if that is the case though.
The split concentric I’ve used does.
One half is neutral, the other half earth.
No gaps.
Exactly, the live conductors are not fully surrounded by earthed metal, neutral conductors are classed as live conductors.
Also split con isn't normally half and half, it's normally at least 2 thirds neutral.
In the UK, the neutral is generally earthed at source, which is why ESQCR allows split con to be buried in the ground.
As the regulation I posted states, it has to have an earthed metallic covering that completely encases the conductors, split con does not therefore unacceptable to be used for the purpose of burying in the wall without rcd protection , mechanical protection etc
Yes, I'm aware it is allowed under ESQCR, and for all practical purposes it will be no different to SWA. However it doesn't satisfy the requirements of bs7671 as far as I know.
Reply to 25mm split con sub main eicr code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Another what code! This is in conjunction with an EICR I have just carried out. 9.5kW shower on 6mm and 32A MCB. Been in place for a long time...
I recently undertook an EICR report for a small house and the conservatory extension had a separate fuseboard which was fed from a 13A plug top...
6K
Hi Im newto this forum and hello to everybody. Im experienced electrician with 15 years of experience in all kind of domestic premised. Some...
6K
Currently quoting for a job that needs to be done next week and working out how best to proceed, so thoughts welcome. Current situation: -->PME...
4K