The requirement to provide RCD protection for cables concealed in walls, was introduced in the 17th.
So nothing was removed in the 16th.
Quite correct error on my part. Nevertheless concentric was but no longer is suitable no matter it's construction.
 
Probably doesn’t comply, because the standards for con and split con are different to those for SWA.

Have heard in the past, that con and split con are prohibited by ESQCR for use in consumer’s installations.
Not sure if that is the case though.
 
The split concentric I’ve used does.
One half is neutral, the other half earth.
No gaps.

Exactly, the live conductors are not fully surrounded by earthed metal, neutral conductors are classed as live conductors.

Also split con isn't normally half and half, it's normally at least 2 thirds neutral.
 
Exactly, the live conductors are not fully surrounded by earthed metal, neutral conductors are classed as live conductors.

Also split con isn't normally half and half, it's normally at least 2 thirds neutral.
In the UK, the neutral is generally earthed at source, which is why ESQCR allows split con to be buried in the ground.
 
In the UK, the neutral is generally earthed at source, which is why ESQCR allows split con to be buried in the ground.
As the regulation I posted states, it has to have an earthed metallic covering that completely encases the conductors, split con does not therefore unacceptable to be used for the purpose of burying in the wall without rcd protection , mechanical protection etc
 
In the UK, the neutral is generally earthed at source, which is why ESQCR allows split con to be buried in the ground.

Yes, I'm aware it is allowed under ESQCR, and for all practical purposes it will be no different to SWA. However it doesn't satisfy the requirements of bs7671 as far as I know.
 

Reply to 25mm split con sub main eicr code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock