Hi, wondering if anyone has seen this before. At a job today and the supply to the 3 phase dust board is 2x16mm armours. One has three phases in it the other armour has the neutral and earth. Bit rough I think is there any regs on this ? Any help would be great.
 
The glands are separate holes and assuming this is a ferrous enclosure then a slot should be cut between them.
 
Unbalanced currents in SWA conductors can cause circulating currents in the armour too. In some situations it is preferable for the armour to be connected at one end only to prevent this. In this case only the neutral current is unbalanced, consisting of up to one full line current and/or the zero sequence harmonics. In reality it's not likely to be a problem but it does have theoretical drawbacks.
 
The Regulations do not permit single core swa cables for ac circuits. You could argue the cable for the neutral and cpc breach this assuming it is referring to live conductors.
 
Large single-core cables are typically AWA rather than SWA, so there is no ferromagnetic component of the cable enclosing a longitudinal current. In any case on the supply side they aren't working to BS7671, which I had forgotten explicitly precluded 1c SWA for AC.
 

Reply to 2armours supplies dist board in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock